<div>Dear all,</div>
<div> </div>
<div>Ihave a question:</div>
<div>The Restaurant Trnflow Example doesn't RUN, it shows "Parameters for Trnflow are missing", then I checked it, obviously, all the Value of Trnflow is 0. Why is it like that? Did the TRNSYS Corporation not SET the Value or  the Parameters are missing after the installtion? Please explain in detail! thanks!</div>

<div> </div>
<div>Br.</div>
<div> </div>
<div>wang<br><br></div>
<div class="gmail_quote">2010/8/4 <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Send TRNSYS-users mailing list submissions to<br>       <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>To subscribe or unsubscribe via the World Wide Web, visit<br>       <a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>       <a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br><br>You can reach the person managing the list at<br>
       <a href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br><br>When replying, please edit your Subject line so it is more specific<br>than "Re: Contents of TRNSYS-users digest..."<br>
<br>Today's Topics:<br><br>  1. Re: TRNSYS-users Digest, Vol 68, Issue 7 (ghetu mariana)<br>  2. Re: Virtual window in TRNBUILD (Marion Hiller)<br>  3. Re: Internal walls and Trnsys3d (Marion Hiller)<br>  4. TRNFlow and COMIS stand-alone version (Marion Hiller)<br>
<br><br>---------- 已转发邮件 ----------<br>From: ghetu mariana <<a href="mailto:ghetu_mariana@yahoo.co.uk">ghetu_mariana@yahoo.co.uk</a>><br>To: <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
Date: Wed, 4 Aug 2010 09:07:03 +0000 (GMT)<br>Subject: Re: [TRNSYS-users] TRNSYS-users Digest, Vol 68, Issue 7<br>
<div>
<div style="FONT-FAMILY: arial, helvetica, sans-serif; FONT-SIZE: 12pt">
<div>
<p class="MsoNormal"><span lang="EN-US">Hello,</span></p>
<p class="MsoNormal"><span lang="EN-US"><br></span></p>
<p class="MsoNormal"><span lang="EN-US">Does anyone know how can I have one iteration per timestep within Type 56? I need to insert something like: Tint(INFO(7)=0) = Tint(INFO(7)=1)</span>.</p>
<p class="MsoNormal"> Is there a way to do this without changing the code of Type 56?</p>
<p class="MsoNormal"><span lang="EN-US"><br></span></p>
<p class="MsoNormal"><span lang="EN-US">Thanks for any info.</span></p>
<p class="MsoNormal"><span lang="EN-US"><br></span></p>
<p class="MsoNormal"><span lang="EN-US">Mariana GHETU</span></p></div>
<div style="FONT-FAMILY: arial, helvetica, sans-serif; FONT-SIZE: 12pt"><br>
<div style="FONT-FAMILY: arial, helvetica, sans-serif; FONT-SIZE: 13px"><font size="2" face="Tahoma">
<hr size="1">
<b><span style="FONT-WEIGHT: bold">From:</span></b> "<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a>" <<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a>><br>
<b><span style="FONT-WEIGHT: bold">To:</span></b> <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br><b><span style="FONT-WEIGHT: bold">Sent:</span></b> Wed, 4 August, 2010 7:05:11<br>
<b><span style="FONT-WEIGHT: bold">Subject:</span></b> TRNSYS-users Digest, Vol 68, Issue 7<br></font><br>Note: Forwarded message is attached.<br><br>Send TRNSYS-users mailing list submissions to<br>    <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<br>To subscribe or unsubscribe via the World Wide Web, visit<br>    <a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>or, via email, send a message with subject or body 'help' to<br>
    <a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a><br><br>You can reach the person managing the list at<br>    <a href="mailto:trnsys-users-owner@cae.wisc.edu" target="_blank">trnsys-users-owner@cae.wisc.edu</a><br>
<br>When replying, please edit your Subject line so it is more specific<br>than "Re: Contents of TRNSYS-users digest..."<br>Today's Topics:<br><br>  1. TRNSYS solar modeling position posted at NREL (Blair, Nate)<br>
  2. Re: modify layer library (David Bradley)<br>  3. Re: Creation of a New Type and Error message 105<br>      (Soteris Kalogirou)<br>_______________________________________________<br>TRNSYS-users mailing list<br><a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br></div></div>
<div></div></div><br></div><br><br>---------- 已转发邮件 ----------<br>From: "Marion Hiller" <<a href="mailto:hiller@transsolar.com">hiller@transsolar.com</a>><br>To: trnsys-users <<a href="mailto:trnsys-users@engr.wisc.edu">trnsys-users@engr.wisc.edu</a>><br>
Date: Wed, 4 Aug 2010 11:19:51 +0200<br>Subject: Re: [TRNSYS-users] Virtual window in TRNBUILD<br>
<div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial">Dear Marcello,</font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial"></font></span>  </div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial">the window in the TESS lib isn't defined correctly.</font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial">I'm not sure if  TESS released a corrected version of the Library.</font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial">Maenwhile you can use the vitual window of the AMERICAN or GERMAN Library.</font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial">they should worl without a problem.</font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial"></font></span>  </div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial">Marion Hiller</font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial"></font></span>  </div>
<div>  </div>
<div align="left"><span style="FONT-FAMILY: arial; COLOR: rgb(0,90,0); FONT-WEIGHT: bold">Dipl.-Ing. Marion Hiller </span><br style="COLOR: rgb(0,153,0); FONT-WEIGHT: bold"><span style="FONT-FAMILY: arial; COLOR: rgb(0,112,0); FONT-WEIGHT: bold">TRANSSOLAR Energietechnik GmbH </span><br style="FONT-FAMILY: arial">
<small><span style="FONT-FAMILY: arial; COLOR: rgb(0,90,0); FONT-WEIGHT: bold"><font size="1">Munich - New York - Stuttgart + 49.711.67976.0 <br style="FONT-FAMILY: arial"></font><small><span style="FONT-FAMILY: arial"></span><br style="FONT-FAMILY: arial">
<span style="FONT-FAMILY: arial; COLOR: rgb(0,0,0); FONT-WEIGHT: bold">KlimaEngineering- Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäuden </span><br style="FONT-FAMILY: arial"><span style="FONT-FAMILY: arial; COLOR: rgb(0,0,0); FONT-WEIGHT: bold">Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart / Amtsgericht Stuttgart - HRB 23347 / USt-IdNr.: 99073/00911 <br style="FONT-FAMILY: arial">
<span style="FONT-FAMILY: arial; COLOR: rgb(0,0,0); FONT-WEIGHT: bold"></span>Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer, Dipl.Phys. Stefan Holst <br></span></small></span></small></div>
<div>  </div><br>
<div dir="ltr" lang="de" align="left">
<hr>
   <font size="2" face="Tahoma"><b>Von:</b> Marcello Caciolo [mailto:<a href="mailto:mcaciolo@hotmail.com" target="_blank">mcaciolo@hotmail.com</a>] <br><b>Gesendet:</b> Freitag, 30. Juli 2010 10:33<br><b>An:</b> <a href="mailto:trnsys-users@engr.wisc.edu" target="_blank">trnsys-users@engr.wisc.edu</a><br>
<b>Betreff:</b> [TRNSYS-users] Virtual window in TRNBUILD<br></font><br></div>
<div></div>
<p>Dear TRNSYS users, <br><br>I am trying to model a zone with an opened window in TRNSYS 16. For the thermal model, I use the type56 with a window of the type: "Virtual (open or nonexistent) Window" (WINID 1) from TESS Library. <br>
<br>Unfortunately, when I start the simulation, I get the following error: <br><br>"Une valeur négative ou supérieure à 1 a été trouvé pour l'absorption non visuelle W4_front pour la fenêtre no 1 : abs_nonvis = -.0008717874 à l'angle = 0" <br>
(A value negative or greater than 1 was found for nonvisual absorption W4_front for Window-ID   1 : abs_nonvis = -.0008717874 at angle = 0) <br><br>I see that other people reported this problem in this forum, but I have not found any solution. <br>
<br>Do you know how to solve this issue? <br><br>Thanks in advance for your attention. <br><br>Best regards, <br><br>Marcello CACIOLO <br><br><span>-- <br></span>-------------------------------------------------------------------------------- <br>
<br>Marcello CACIOLO <br>Ingénieur de Recherche  Centre Energétique et Procédés - Mines ParisTech <br>60, Bd Saint-Michel  75272 Paris Cedex 06 France  <br>Tél : +33 (0)1 40 51 94 21 Fax : +33 (0)1 40 51 94 49 <br>E-mail: <a href="mailto:marcello.caciolo@ensmp.fr" target="_blank">marcello.caciolo@ensmp.fr</a> <br>
<br>-------------------------------------------------------------------------------- </p></div><br><br>---------- 已转发邮件 ----------<br>From: "Marion Hiller" <<a href="mailto:hiller@transsolar.com">hiller@transsolar.com</a>><br>
To: trnsys-users <<a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>Date: Wed, 4 Aug 2010 11:28:06 +0200<br>Subject: Re: [TRNSYS-users] Internal walls and Trnsys3d<br>
<div lang="ES" link="blue" vlink="purple">
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">Dear Pablo,</font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span>  </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">the 3D detailed radiation mode of TRNSYS 17 are restricted to convexe zones. </font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">Therefore no "internal walls" blocking views are allowed to be defined.</font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span>  </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">You may split your zone into convex several convex zones or increase the capacity of the air node.</font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span>  </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">At the moment we are working on developing and incoorperating improved algorithms which can </font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">handle concave zones</font></span><span><font color="#0000ff" size="2" face="Arial">. </font></span></div>
<div dir="ltr" align="left"><span></span><span><font color="#0000ff" size="2" face="Arial"></font></span><span><font color="#0000ff" size="2" face="Arial"></font></span>  </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">Marion</font> </span> </div><br>
<div dir="ltr" lang="de" align="left">
<hr>
   <font size="2" face="Tahoma"><b>Von:</b> Direccion [mailto:<a href="mailto:direccion@idienergia.es" target="_blank">direccion@idienergia.es</a>] <br><b>Gesendet:</b> Dienstag, 3. August 2010 13:56<br><b>An:</b> <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<b>Betreff:</b> [TRNSYS-users] Internal walls and Trnsys3d<br></font><br></div>
<div></div>
<p>
<div>
<p class="MsoNormal"><span lang="EN-US">Hello.</span> </p>
<p class="MsoNormal"><span lang="EN-US"> </span> </p>
<p class="MsoNormal"><span lang="EN-US">There’s no “internal wall” in “Constructions”  when I try to draw a building with Trnsys3d. I can’t add that walls inside Trnbuild 17, because I need to use the 3D Model. </span></p>

<p class="MsoNormal"><span lang="EN-US">¿Somebody knows how can I model these types of walls and, at the same time, model with Trnsys 3D?</span> </p>
<p class="MsoNormal"><span lang="EN-US"> </span> </p>
<p class="MsoNormal"><span lang="EN-US">Thanks to all.</span> </p>
<p class="MsoNormal"><span lang="EN-US"> </span> </p>
<p class="MsoNormal"><span lang="EN-US">PABLO EGUÍA</span> </p>
<p class="MsoNormal"><span lang="EN-US">Director Técnico</span> </p>
<p class="MsoNormal"><span lang="EN-US">IDi Energia.</span> </p>
<p class="MsoNormal">C/Padre Ramón María Aller, nº 6, 1ºD </p>
<p class="MsoNormal">36201 – VIGO </p>
<p class="MsoNormal">Pontevedra </p></div>
<p></p>
<p></p></p></div><br><br>---------- 已转发邮件 ----------<br>From: "Marion Hiller" <<a href="mailto:hiller@transsolar.com">hiller@transsolar.com</a>><br>To: trnsys-users <<a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>
Date: Wed, 4 Aug 2010 11:46:09 +0200<br>Subject: [TRNSYS-users] TRNFlow and COMIS stand-alone version<br>
<div>
<div dir="ltr" align="left"><font color="#0000ff" size="2" face="Arial"><span>Dear Wang,</span></font> </div>
<div dir="ltr" align="left"><font color="#0000ff" size="2" face="Arial"><span></span></font>  </div>
<div dir="ltr" align="left"><font color="#0000ff" size="2" face="Arial"><span>TRNFlow is an integrated version of COMIS into Type 56. </span></font></div>
<div dir="ltr" align="left"><font color="#0000ff" size="2" face="Arial"><span></span></font><font color="#0000ff" size="2" face="Arial"><span>If you want use TRNbuild/TRNFlow you need to define your airflow network within TRNBuild.</span></font> </div>

<div dir="ltr" align="left"><font color="#0000ff" size="2" face="Arial"><span>Within the Studio create a multizone building project. You don't need a COMIS version at all.</span></font> </div>
<div dir="ltr" align="left"><font color="#0000ff" size="2" face="Arial"><span></span></font>  </div>
<div dir="ltr" align="left"><font color="#0000ff" size="2" face="Arial"><span>For using the stand-alone version of COMIS in TRNSYS, the option create "COMIS project" of the Studio can be used.</span></font> </div>

<div dir="ltr" align="left"><font color="#0000ff" size="2" face="Arial"><span></span></font>  </div>
<div dir="ltr" align="left"><font color="#0000ff" size="2" face="Arial"><span>Marion</span></font> </div>
<div dir="ltr" align="left"><font color="#0000ff" size="2" face="Arial"><span></span></font>  </div>
<div dir="ltr" align="left">
<hr>
   <font size="2" face="Tahoma"><b>Von:</b> 王洋 [mailto:<a href="mailto:wanghongyang1767@gmail.com" target="_blank">wanghongyang1767@gmail.com</a>] <br><b>Gesendet:</b> Freitag, 30. Juli 2010 18:13<br><b>An:</b> <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<b>Betreff:</b> Re: [TRNSYS-users] TRNSYS-users Digest, Vol 67, Issue 68<br></font><br></div>
<div></div>
<div>
<p>hi every one! </p></div>
<div>  </div>
<div>I build a COMIS project, but it shows "the full version of COMIS is not installed correctly, the demo version be used......." How to make it? I had TRNSYS/TRNFLOW.<br> <br>thans! </div>
<div>  </div>
<div>wang<br><br></div>
<div class="gmail_quote">2010/7/29 <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a>></span><br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Send TRNSYS-users mailing list submissions to<br>       <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<br>To subscribe or unsubscribe via the World Wide Web, visit<br>       <a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>       <a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a><br><br>You can reach the person managing the list at<br>
       <a href="mailto:trnsys-users-owner@cae.wisc.edu" target="_blank">trnsys-users-owner@cae.wisc.edu</a><br><br>When replying, please edit your Subject line so it is more specific<br>than "Re: Contents of TRNSYS-users digest..."<br>
<br>Today's Topics:<br><br>  1. Re: TRNSYS-users Digest, Vol 67, Issue 65 (Jeff Thornton)<br><br><br></blockquote></div></div><br>_______________________________________________<br>TRNSYS-users mailing list<br><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br><br></blockquote></div><br>