<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.01 Transitional//EN">
<html>
<head>
  <meta content="text/html; charset=ISO-8859-1"
 http-equiv="Content-Type">
</head>
<body bgcolor="#ffffff" text="#000000">
Guy,<br>
 Unfortunately, I don't know the answer to your question directly.
However, I suspect that since radiation can be transmitted, absorbed,
or reflected, by definition, the radiation absorbed on outside surfaces
would NOT include any that was transmitted through the outside surface
into the interior of the zone. The TRNSYS 17 manual offers the
following clarification:<br>
<br>
SQABSO is the total radiation absorbed at the outside surfaces of
specified airnodes (thermal zones in TRNSYS 16) including solar gains,
radiant heat, internal radiation and wallgains, but not longwave
radiation exchange with Tsky.<br>
<br>
If I am incorrect in this, please do correct me!<br>
Best,<br>
 David<br>
<br>
<br>
<br>
On 7/28/2010 08:19, Guy THOMAS wrote:
<blockquote cite="mid:BLU110-W176B0A3558A260610906D1D7A80@phx.gbl"
 type="cite">
  <style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 10pt;
font-family:Verdana
}
--></style>Hi,<br>
I would like to know if the output 45 "SQABSO" (Sum of total radiation
absorbed at all outside surfaces for group of zones) includes the solar
radiation transmitted through windows or do I have to add the output 42
"SQSOLT" to have all the radiations from outside?<br>
Kind regards<br>
Guy THOMAS<br>
  <br>
  <hr>Envie de nouveauté ? <a moz-do-not-send="true"
 href="http://www.windowslive.fr/nouveau-hotmail/" target="_new">Le
nouveau Hotmail arrive bientôt ! Préparez-vous !</a>
  <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
  </pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:bradley@tess-inc.com">bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>