<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.01 Transitional//EN">
<html>
<head>
  <meta content="text/html; charset=ISO-8859-1"
 http-equiv="Content-Type">
</head>
<body bgcolor="#ffffff" text="#000000">
Mavi,<br>
  I faced this same situation at one point and was able to use Type505
by turning it around backwards. Fundamentally, when Type505 refers to
"heating," it is heating the air stream and cooling the water stream.
When it is "cooling" it is cooling the air and heating the water
stream. In your case, "heating" means heating the water and cooling the
air. So if you treat Type505's "cooling" control signal as though it
were your "heating" control signal, it should work fine.<br>
<br>
 I believe that in upcoming Tess Libraries 17, there is a specific
component for what you are trying to do but I am not aware of its
status at the moment.<br>
Best,<br>
 david<br>
<br>
<br>
On 7/7/2010 07:06, Mavi Cambronero Vázquez wrote:
<blockquote
 cite="mid:AANLkTinxL9VRxCDVpuXDeyLE_5BdI0NRLHyrBqdieexJ@mail.gmail.com"
 type="cite">
  <div>Hi all!</div>
  <div> </div>
  <div>I´m looking for a typical air-water heat pump. I have HVAC
library from TESS but the type that is called water-source heat pump is
not what I need. The scheme is the same but the fluid stream and the
air stream air in opposite places, that is, if I want to simulate a
conventional heat pump in order to cool the air inside a building what
I need to cool is the liquid stream that would be indoor. In that case,
the air flow would be outdoor. Type 505 is what Ì´d need but exchanging
both streams.</div>
  <div> </div>
  <div>I don´t know if I explained well my problem. Does anybody know
the correct type to simulate an air-water heat pump, with the water
stream indoor?</div>
  <div> </div>
  <div>Thanks in advance.</div>
  <div> </div>
  <div>Best,</div>
  <div> </div>
  <div>Mavi</div>
  <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
  </pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:bradley@tess-inc.com">bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>