<br><font size=3>It is likely that this error is caused by some of the
inputs to Type 33. I suggest you check the data in your weather file for
unrealistic values. The source of the error can also be some other component
which calls the PSYCHROMETRICS routine, for example Type 56 and various
HCAC components. In the List-file, where the error is mentioned, there
should also be Type and/or unit number for the component(s) caussing the
error. If you find any other components listed here, I suggest you check
their inputs with an online plotter. Try to notice the time when the error
occurs, if this coincides with turning on heating/cooling, for example.</font>
<br>
<br><font size=3>Hope that some of this turns out helpful.</font>
<br>
<br><font size=3>Best regards,</font>
<br><font size=3>Knut Erik Enerstvedt</font>
<br>
<br><font size=4>>Dear all<br>
<br>
>i get that error message</font><font size=3><br>
</font><font size=4><br>
>TRNSYS Message    118 : The subroutine SAT of the utility
routine PSYCHROMETRICS, which >calculates the thermodynamic properties
of moist air, has been called with a temperature below >absolute zero
(-273 C).  Please check the TYPE routine which calls the psychrometrics
routine for >possible sources of errors.</font><font size=3><br>
</font><font size=4><br>
>someone can help me? i connect type 33e  to type 109b and type
69b<br>
<br>
>Many thanks<br>
<br>
>Ivan Tombolato</font><font size=2 face="sans-serif"><br>