<br><font size=2 face="sans-serif">Hello Mehdi,</font>
<br>
<br><font size=2 face="sans-serif">You can use a forcing function (Type
14) and an equation block to solve this issue. Step 1: Set the forcing
function to output 0 for the hours of the year you define as winter and
1 for the hours you define as summer. Step 2: In an equation block with
an input variable "Summer" from the forcing function, define
two equations "c_coil_ctrl = Summer" and "h_coil_ctrl =
1 - Summer". Step 3: Link "c_coil_ctrl" to all control signals
concerning the cooling coil (pumps, fans etc.) and "h_coil_ctrl"
to all control signals concerning the heating coil. This will run the cooling
coil in summer and heating coil in winter.</font>
<br>
<br><font size=2 face="sans-serif">Best regards,</font>
<br><font size=2 face="sans-serif">Knut Erik Enerstvedt </font>
<br>
<br>
<br><font size=2 color=#800080 face="sans-serif">----- Message from mahdi
shahrestani <mahdishahrestani@yahoo.com> on Sat, 5 Jun 2010 18:08:23
-0700 (PDT) ----</font>
<table>
<tr>
<td>
<div align=right></div>
<td>
<tr>
<td>
<div align=right></div>
<td></table>
<br><tt><font size=2>>Hello everybody <br>
<br>
>My project has two main parts, first cooling coil and the second heating
coil. I want to run the cooling coil in summer >and heating coil in
winter. <br>
<br>
>As far as I know, start and stop run time in “control card” are applicable
to all equipment but I need to run cooling part >in summer and heating
parts in winter.<br>
>I was wondering if any body could give me some hint to solve the issue.
<br>
<br>
>Regards<br>
>Mehdi<br>
<br>
</font></tt>