<br><tt><font size=2>Hello,</font></tt>
<br>
<br><tt><font size=2>The example datafile for Type 655 is incorrect. The
first column in the datafile should be COP ratios and the second column
should be capacity ratios, not the other way round as in the example file.
You can check the source code for Type 655 to see this. Try switching the
two columns and you should see a change in COP.</font></tt>
<br>
<br><tt><font size=2>Kind regards,</font></tt>
<br><tt><font size=2>Knut Erik Enerstvedt</font></tt>
<br>
<br>
<br>
<br><tt><font size=2>>Hello everybody <br>
<br>
>I have problem in using type 655 Air cooled chiller. It is strange
when I change the ambient and chilled >water set point temperature neither
COP and Power consumption would be changed. <br>
>It is clear that the cop and energy consumption should be change by
those two parameters but it is another >strange element in Trnsys.<br>
<br>
>I was wondering if you could give me a clue to tackle it.<br>
<br>
>Many thanks for your time <br>
>Mehdi Shahrestani</font></tt><font size=2 face="sans-serif"><br>
------------------------------------------------------------------------------------------------------------<br>
Meld deg på vårt nyhetsbrev på </font><a href=www.niva.no><font size=2 face="sans-serif">www.niva.no</font></a>