<div>Thanks for your answers.....</div>
<div><br>I´ve noticed that the problem is the chilled ceiling used. It´s the first time that I try to use it and I supose I didn´t succeed. I know how to create a chilled ceiling layer, but I´m not sure what are the following steps. What I did was integrate the new layer as the last one in a new wall. TRNBuild said to me that a wall with chilled ceiling can´t be external, boundary or internal, so the only option is that it is adjacent.... adjacent to the roof???So I created a new zone called roof! I´m a bit confused.</div>
<div> </div>
<div>If someone could help me I´d be very grateful!</div>
<div> </div>
<div>Thanks</div>
<div><br> </div>
<div class="gmail_quote">2010/4/29 <span dir="ltr"><<a href="mailto:knut.erik.enerstvedt@niva.no">knut.erik.enerstvedt@niva.no</a>></span><br>
<blockquote class="gmail_quote" style="PADDING-LEFT: 1ex; MARGIN: 0px 0px 0px 0.8ex; BORDER-LEFT: #ccc 1px solid"><br><font face="Arial" color="#000080" size="2">In addition to reducing time step length, I would try the following:</font> <br>
<br><font face="Arial" color="#000080" size="2">- Check if there is sufficient thermal mass in your system (add pipes in fluid loops, for example).</font> <br><font face="Arial" color="#000080" size="2">- Use controllers (such as Type 2) instead of equations (LT, GT and similar) when variables that can change from one iteration to the next are involved.</font> <br>
<font face="Arial" color="#000080" size="2">- Place components in a "natural" calling order (controllers before controlled equipment, for example): Control cards->Component order: Click and drag the different components to order them.</font> <br>
<font face="Arial" color="#000080" size="2">- Use an online plotter to check if there are any unrealistic output values (very high temperatures, for example).</font> <br>
<div class="im"><br><font face="Arial" color="#000080" size="2">Best regards,</font> <br><font face="Arial" color="#000080" size="2">Knut Erik Enerstvedt</font> <br><br><br><br><br></div>
<div class="im"><font face="Arial" color="#000080" size="2">>You could change the simulation time step (in steps of 1/(2^n) so 1 hour, 0,5 hour, 0,25 hour etc). You can find this by assembly -> component >order.</font> <br>
<font face="Arial" color="#000080" size="2"> </font> <br><font face="Arial" color="#000080" size="2">>Good luck,</font> <br><font face="Arial" color="#000080" size="2"> </font> <br><font face="Arial" color="#000080" size="2">>Mariëlle Nuchelmans</font> <br>
<font face="Times New Roman" size="3"> </font> <br><font face="Times New Roman" size="3"> </font> <br></div>
<div class="im"><font face="Times New Roman" size="3">>Hi,</font> <br><font face="Times New Roman" size="3"> </font> <br><font face="Times New Roman" size="3">>What can I do when there are lots of convergence problems??? The same project has different warnigs because of that if the simulation >starts at 3896 than if it starts at 0.... Does the option "Optimaze component order" work?? If I select that option other errors appear... :(</font></div>
<div>
<div></div>
<div class="h5"><font face="sans-serif" size="2"><br>------------------------------------------------------------------------------------------------------------<br>Meld deg på vårt nyhetsbrev på </font><a href="http://www.niva.no/" target="_blank"><font face="sans-serif" size="2">www.niva.no</font></a></div>
</div></blockquote></div><br>