<br><tt><font size=2>You are absolutely right about this. There is a mismatch
between documentation and example datafile on one side and source code
on the other. The first column in the datafile should consist of COP ratios,
while the second column should consist of capacity ratios. There have been
some postings about this on the list in the past.</font></tt>
<br>
<br><tt><font size=2>Best regards,</font></tt>
<br><tt><font size=2>Knut Erik Enerstvedt</font></tt>
<br>
<br><tt><font size=2> </font></tt>
<br>
<br><tt><font size=2>>Hello, all.<br>
<br>
>I previously developed a parametric model for a water-cooled chiller.
I used it<br>
>to compare the results with those based on Type666. I then found
that<br>
>calculated COP seemed to increase only mildly during the low-load period
when<br>
>using Type666. I went through the source code and the related
data files. I<br>
>found that the following statements appeared to be wrong:<br>
<br>
>COP_RATIO=Y(1)<br>
>CAP_RATIO=Y(2)<br>
<br>
>According to the data file, the first output should be the capacity
ratio while<br>
>the second output is the COP ratio. The same case happened for
Type655. Am I<br>
>wrong?<br>
<br>
>Best Regards<br>
>LEE, Chun Kwong<br>
>Division of Building Science and Technology<br>
>City University of Hong Kong</font></tt><font size=2 face="sans-serif"><br>