<div class="gmail_quote">David,<br>I am trying to define the cooling capacity of the ceiling panel. This could be determined by the following equation:<br><br>Q=m*c<font size="1">p</font>*(θout-θin)<br><br>I expected that changing the water flowrate and/or the water inlet temperature , the program would give me as an output the fluid outlet temperature (θout in the above equation).Using the above equation i could obtain useful results for the expected thermal behaviour of such a system (that is to say, if it does meet the cooling needs of the zone).<br>

<br>So , is there anywhere in the program the answer i am looking for (the fluid oulet temperature)?<br><br><b><u>Second thought</u></b><br><br>The designers of the ceiling panels say that these systems are designed for a temperature difference (of chilled water) about 2-4 K. If this is the case for the program as well, I expected to define this temperature difference somewhere in the program. Taking for granted that the cooling load equals to cooling capacity of the ceiling panel, I could then determine the mass flowrate needed.<br>

<br>Thank you for your answer.I hope I made clear the problem.Are there any suggestions?<br><br>Best,<br><div class="im">Dimitris<br>
  <br>
National Technical University Of Athens<br>
School of Mechanical Engineering<br>
Thermal Section<br><br></div><div class="gmail_quote">Στις 02 Μαρτίου 2010 12:36 π.μ., ο χρήστης David Bradley <span dir="ltr"><<a href="mailto:bradley@tess-inc.com" target="_blank">bradley@tess-inc.com</a>></span> έγραψε:<div>
<div></div><div class="h5"><br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">



  

<div bgcolor="#ffffff" text="#000000">
Dimitris,<br>
  Is it the cooling capacity of the chiller or of the ceiling that you
are trying to define?<br>
Best,<br>
 David<br>
<br>
<br>
Δημήτρης Ξεύγενος wrote:
<blockquote type="cite"><div><div></div><div>
  <div class="gmail_quote">Dear TRNSYS users,<br>
  <br>
I am working on a solar cooling project using an absorption chiller and
the new feature of TYPE 56 (regarding to chilled ceilings). <br>
How can i define the cooling capacity as i don't know the fluid outlet
temperature?<br>
Moreover,when i have to define the wall with the cooled ceiling layer ,
it is obligatory to define some parameters that are obtained by the
producer of the cooled ceiling (specific norm power,norm massflow, norm
area, norm number of loops)<br>
Does this definition affect the cooling capacity i mentioned
earlier?Could anyone send me these technical data from any producer
available?<br>
  <br>
Thank you in advance,<br>
Xevgenos Dimitris<br>
  <br>
National Technical University Of Athens<br>
School of Mechanical Engineering<br>
Thermal Section<br>
  </div>
  <br>
  </div></div><pre><hr width="90%" size="4">
_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><div>
<a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
  </div></pre>
</blockquote>
<br>
<pre cols="72">-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: <a href="mailto:bradley@tess-inc.com" target="_blank">bradley@tess-inc.com</a> 
Web Pages:  <a href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>    and      <a href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a>

***********************************************************************</pre>
</div>

</blockquote></div></div></div><br>
</div><br>