Manuel, <br>
  The only way is to change the source code and move the parameter to
an input, then recompiling the Type. The TRNSYS engine reads parameters
from the input file at the beginning of the simulation and stores them
internally. They are never reread so while you can make a parameter
value that is the result of a time dependent equation, only the initial
result of that equation at the very start of the simulation will be
used for the parameter value.<br>
Best,<br>
 David<br>
<br>
<br>
Manuel Daconceicao wrote:
<blockquote
 cite="mid:C77554652705C543BE9C49FA504A6EB8122C42@SERVEUR.Matriciel.local"
 type="cite">
  <meta http-equiv="Content-Type" content="text/html; ">
  <meta name="Generator" content="Microsoft Word 12 (filtered medium)">
  <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:"Arial Narrow";
        panose-1:2 11 6 6 2 2 2 3 2 4;}
@font-face
        {font-family:Webdings;
        panose-1:5 3 1 2 1 5 9 6 7 3;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
span.EmailStyle17
        {mso-style-type:personal-compose;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;}
@page Section1
        {size:612.0pt 792.0pt;
        margin:70.85pt 70.85pt 70.85pt 70.85pt;}
div.Section1
        {page:Section1;}
-->
  </style>
<!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1" />
 </o:shapelayout></xml><![endif]-->
  <div class="Section1">
  <p class="MsoNormal"><span lang="EN-US">Hello,<o:p></o:p></span></p>
  <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
  <p class="MsoNormal"><span lang="EN-US">I see in the TRNSys docs that
variables
used in place of numerical values for parameter can’t be time-dependent
quantities. However I use the Tess’ Type661, with parameter that’s
depending on the time (# of timestep to hold value).<o:p></o:p></span></p>
  <p class="MsoNormal"><span lang="EN-US">Is it possible to make this
parameter is
considered like an input?  I could make several versions of this
Type661 and
add an equation that chooses the right output depending on the time but
it’s
not possible because it will make too lots of trnsys modules.<o:p></o:p></span></p>
  <p class="MsoNormal"><span lang="EN-US">So this solution is not
possible right here
right now. Is there another solution for me? <o:p></o:p></span></p>
  <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
  <p class="MsoNormal"><span lang="EN-US">Thank you in advance for your
help.<o:p></o:p></span></p>
  <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
  <p class="MsoNormal"><span lang="EN-US">Manu<o:p></o:p></span></p>
  <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
  <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
  <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
  <p class="MsoNormal"><b><span
 style="font-size: 13.5pt; font-family: "Arial Narrow","sans-serif"; color: gray;">MATRI<i>ciel</i></span></b><b><span
 style="font-family: "Arial Narrow","sans-serif";">
  <span style="color: gray;">sa</span></span></b><span
 style="font-size: 12pt; font-family: "Arial Narrow","sans-serif"; color: gray;"><o:p></o:p></span></p>
  <p class="MsoNormal"><b><span
 style="font-size: 10pt; font-family: "Arial Narrow","sans-serif"; color: gray;">Ir
Manuel da Conceição Nunes</span></b><b><span
 style="font-size: 10pt; font-family: "Arial Narrow","sans-serif"; color: black;">
  </span></b><b><span
 style="font-size: 10pt; font-family: "Arial Narrow","sans-serif"; color: gray;"><br>
  </span></b><b><span
 style="font-size: 8pt; font-family: "Arial Narrow","sans-serif"; color: gray;">                                         </span></b><b><span
 style="font-family: "Arial Narrow","sans-serif"; color: gray;"><br>
  </span></b><span
 style="font-size: 8pt; font-family: "Arial Narrow","sans-serif"; color: gray;">Place
de l'Université, 25 Etage 2 à 1348 Louvain-la-Neuve<br>
Tél : 010/24 15 70 - Fax : 010/24 15 60 <o:p></o:p></span></p>
  <p class="MsoNormal"><a moz-do-not-send="true"
 href="mailto:daconceicao@matriciel.be"><span
 style="font-size: 8pt; font-family: "Arial Narrow","sans-serif"; color: gray;">daconceicao@matriciel.be</span></a><span
 style="font-size: 8pt; font-family: "Arial Narrow","sans-serif"; color: gray;"><br>
  </span><a moz-do-not-send="true" href="http://www.matriciel.be/"
 title="blocked::http://www.matriciel.be/
http://www.matriciel.be"><span
 style="font-size: 8pt; font-family: "Arial Narrow","sans-serif"; color: gray;">http://www.matriciel.be</span></a><span
 style="font-size: 8pt; font-family: "Arial Narrow","sans-serif"; color: blue;"><o:p></o:p></span></p>
  <p class="MsoNormal"><b><span
 style="font-size: 14pt; font-family: Webdings; color: rgb(153, 204, 0);"
 lang="EN-GB">P</span></b><b><span
 style="font-size: 14pt; font-family: "Arial","sans-serif"; color: olive;"
 lang="EN-GB"> </span></b><b><span
 style="font-size: 8pt; font-family: "Arial","sans-serif"; color: olive;"
 lang="EN-GB">
  </span></b><b><span
 style="font-size: 7pt; font-family: "Arial","sans-serif"; color: rgb(153, 204, 0);"
 lang="EN-GB">Please consider your environmental responsibility before
printing this e-mail</span></b><span
 style="font-size: 8pt; font-family: "Times New Roman","serif";"
 lang="EN-GB"><o:p></o:p></span></p>
  <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
  </div>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
  </pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: <a class="moz-txt-link-abbreviated" href="mailto:bradley@tess-inc.com">bradley@tess-inc.com</a> 
Web Pages:  <a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>    and      <a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a>
***********************************************************************</pre>
</body>
</html>