Maarten, Sabine,<br>
<br>
This is accomplished by a reverse approach.  Set the heating or cooling
air setpoint temperature with type 56 as an input.  Then, you can use
an equation in the dck to calculate this variable setpoint temperature
(e.g. the air temperature required to achieve your operative
temperature setpoint, based on the current mean radiant temperature).<br>
<br>
Erik<br>
<br>
<div class="moz-signature">
<title></title>
<font style="color: rgb(128, 128, 128);" align="left"><font align="left"><font
 face="Arial" size="1">Erik Olsen, PE</font><font face="Arial" size="1"><br>
</font><font face="Arial" size="1">212 219 2255</font></font></font><font
 style="color: rgb(128, 128, 128);" align="left"><font align="left"><font
 face="Arial" size="1"> | <a class="moz-txt-link-abbreviated" href="mailto:olsen@transsolar.com">olsen@transsolar.com</a><br>
</font></font></font><font style="color: rgb(128, 128, 128);"
 align="left"><font align="left"><font face="Arial" size="1">Transsolar
Inc. | 134 Spring St. Suite 601 | New
York, NY 10012<br>
<br>
</font></font></font><font style="color: rgb(128, 128, 128);"
 align="left"><font align="left"><font face="Arial" size="1">Transsolar
Climate Engineering<br>
Technical consulting for energy efficiency and environmental quality in
buildings<br>
</font><font face="Arial" size="1">New York - Stuttgart - Munich</font></font></font>
</div>
<br>
<br>
Sabine Jansen - BK wrote:
<blockquote
 cite="mid:%3C7F4254B1CE71C84596250D072736AF8915DDD8@SRV503.tudelft.net%3E"
 type="cite">
  <title>[TRNSYS-users] Simplified heating and cooling based on
operativetemperature</title>
  <meta content="text/html; charset=unicode" http-equiv="Content-Type">
  <meta name="GENERATOR" content="MSHTML 8.00.6001.18876">
  <div dir="ltr" id="idOWAReplyText40328">
  <div dir="ltr"><font color="#000000" face="Arial" size="2">Dear all,</font></div>
  <div dir="ltr"> </div>
  <div dir="ltr"><font face="Arial" size="2">I am also interensted in
that question.</font></div>
  <div dir="ltr"> </div>
  <div dir="ltr"><font face="Arial" size="2">The only way I know now
how to solve this is by using a type (controller, type 2 or thermostat,
type 8) outside type 56. The the operative zone temperature must be
connected to this type (e.g. 2b and creating a schedule elsewhere, in
an equation solver), and the heating must be defined as a limited power
connected to an input, which is then the output of the control type
(type 2 or type 8).</font></div>
  <div dir="ltr"> </div>
  <div dir="ltr"><font face="Arial" size="2">One problem with this
approach is that I cannot use a very large heating power anymore, since
that causes the controller to switch on and off. Thus the heating power
must be determined using the ideal heating, based on air temperature,
first.</font></div>
  <div dir="ltr"> </div>
  <div dir="ltr"><font face="Arial" size="2">If there is an easier way,
I am also very happy.</font></div>
  <div dir="ltr"> </div>
  <div dir="ltr"> </div>
  <div dir="ltr"><font face="Arial" size="2">Kind regards,</font></div>
  <div dir="ltr"> </div>
  <div dir="ltr"><font face="Arial" size="2">Sabine Jansen</font></div>
  </div>
  <div dir="ltr"><br>
  <hr tabindex="-1">
  <font face="Tahoma" size="2"><b>Van:</b> Maarten Sourbron
[<a class="moz-txt-link-freetext" href="mailto:Maarten.Sourbron@mech.kuleuven.be">mailto:Maarten.Sourbron@mech.kuleuven.be</a>]<br>
  <b>Verzonden:</b> do 18-2-2010 13:53<br>
  <b>Aan:</b> <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
  <b>Onderwerp:</b> [TRNSYS-users] Simplified heating and cooling based
on operativetemperature<br>
  </font><br>
  </div>
  <div>
  <p><font size="2">Dear all,<br>
  <br>
The simplified heating and cooling in Trnbuild is now comparing the zone<br>
AIR temperature with the given set points.  Is there a way to change<br>
this (or another controller model) to have the zone OPERATIVE<br>
temperature compared with the set points?<br>
  <br>
Kind regards,<br>
  <br>
Maarten Sourbron<br>
  <br>
--<br>
Departement Werktuigkunde-Department of Mechanical Engineering<br>
Katholieke Universiteit Leuven<br>
Celestijnenlaan 300A bus 2421<br>
3001 Heverlee (Leuven)<br>
T : 0032 (0)16 32 28 73<br>
F : 0032 (0)16 32 29 85<br>
E : <a class="moz-txt-link-abbreviated" href="mailto:Maarten.Sourbron@mech.kuleuven.be">Maarten.Sourbron@mech.kuleuven.be</a><br>
  <br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
  <a moz-do-not-send="true"
 href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
  </font></p>
  </div>
</blockquote>
</body>
</html>