<br><font size=2 face="sans-serif">Paul,</font>
<br>
<br><font size=2 face="sans-serif">When you specify a heating type in TRNBUILD,
you simulate the building in Energy Rate Control. This is useful for dimensioning
equipment as you can output the heating load from the building given a
specific set temperature. When you actually want to simulate operation
of the equipment, like a GSHP system, you should use Temperature Level
Control instead. Then you should turn Heating off in your building zone,
and use Ventilation (if heat is delivered by air) or Gains (for example
radiators or heat pipes) to couple your heat source to the building. See
this tutorial: </font><a href=http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tlc_tutorial.pdf><font size=2 face="sans-serif">http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tlc_tutorial.pdf</font></a><font size=2 face="sans-serif">
for an explanation of using Temperature Level Control.</font>
<br>
<br><font size=2 face="sans-serif">Hope this helps,</font>
<br>
<br><font size=2 face="sans-serif">Knut Erik</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">trnsys-users-request@cae.wisc.edu</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">trnsys-users@cae.wisc.edu</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">09/17/2009 12:24 PM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">TRNSYS-users Digest, Vol 57, Issue 28</font></table>
<br>
<hr noshade>
<br><tt><font size=2><br>
</font></tt><font size=2 color=#800080 face="sans-serif"><br>
----- Message from PAUL COALES <coalespr@btinternet.com> on Thu,
17 Sep 2009 10:16:22 +0000 (GMT) -----</font>
<table>
<tr>
<td>
<div align=right><font size=3><b>To:</b></font></div>
<td><font size=3>Olivier Guillemot <oguillemot@polenn.com></font>
<tr>
<td>
<div align=right><font size=3><b>cc:</b></font></div>
<td><font size=3>trnsys-users@cae.wisc.edu</font>
<tr>
<td>
<div align=right><font size=3><b>Subject:</b></font></div>
<td><font size=3>Re: [TRNSYS-users] TRNBuild / Type56: Documentation on
handling custom inputs</font></table>
<br>
<table>
<tr valign=top>
<td><font size=3 face="Calibri">Thanks for your quick reply Olivier.<br>
<br>
The following paragraph from 06-multizonebuilding.pdf confuses me:<br>
<br>
"The heating requirement of any zone subject to idealized heating
control can be determined by specifying a heating type. If the heating
equipment is modelled external to the TYPE 56 component, the heating type
should not be used. Instead, VENTILATION AIRCHANGE, TEMPERATURE and HUMIDITY
should be defined as INPUTS, fed by outputs from the conditioning equipment
component(s) or the supplied heating power should be defined as CONVECTIVE
and RADIATIVE GAINS. The specification of a heating control is optional
and the default setting of the heating control is off."</font>
<p>
<p><font size=3 face="Calibri">So I do use the Heating Regime to couple
the heat source: I just have to understand the radiative and convective
split of my emitter?</font>
<p>
<p><font size=3 face="Calibri">What role does the “set temperature” provide?
Zone temperature is an output to my simulation and it is the simulation
that controls whether the emitter is receiving heat or not.</font>
<p>
<p><font size=3 face="Calibri">Thanks</font>
<p><font size=3 face="Calibri">Paul </font>
<br><font size=3 face="Calibri"><br>
--- On <b>Thu, 17/9/09, Olivier Guillemot <i><oguillemot@polenn.com></i></b>
wrote:</font>
<br><font size=3 face="Calibri"><br>
<br>
<br>
<br>
<br>
From: Olivier Guillemot <oguillemot@polenn.com><br>
Subject: RE: [TRNSYS-users] TRNBuild / Type56: Documentation on handling
custom inputs<br>
To: "'PAUL COALES'" <coalespr@btinternet.com>, trnsys-users@cae.wisc.edu<br>
Date: Thursday, 17 September, 2009, 10:35 AM<br>
</font>
<p><font size=3 color=#004080 face="Calibri">Paul,</font>
<p><font size=3 color=#004080 face="Calibri">After having created your
input, you can use it in several screens in trnbuild, it depends what you
want to do. </font>
<p>
<p><font size=3 color=#004080 face="Calibri"> </font>
<p><font size=3 color=#004080 face="Calibri"> </font>
<p><font size=3 color=#004080 face="Calibri">Cordialement,</font>
<p><font size=3 color=#004080 face="Calibri"> </font>
<p><font size=3 color=#004080 face="Calibri">Olivier Guillemot</font>
<p><font size=1 color=#004080 face="Calibri">_______________________________</font>
<p><font size=1 color=#004080 face="Calibri">POLENN</font>
<p><font size=1 color=#004080 face="Calibri"><i>Ingénierie de la performance
énergétique</i></font>
<p><a href=http://www.polenn.com/ target=_blank><font size=1 color=blue face="Calibri"><u>www.polenn.com</u></font></a>
<p><font size=1 color=#004080 face="Calibri"><i> </i></font>
<p><font size=1 color=#004080 face="Calibri">Immeuble Oméga</font>
<p><font size=1 color=#004080 face="Calibri">Rue Jean-Marie David, </font>
<p><font size=1 color=#004080 face="Calibri">35 740 Pacé</font>
<p><font size=1 color=#004080 face="Calibri">Tel: 02 23 46 14 36</font>
<p><font size=1 color=#004080 face="Calibri">Fax: 02 90 92 00 71</font>
<p><a href=http://www.polenn.com/ target=_blank><img src=cid:_2_07F17D9007F17A5C003D90B3C1257634 alt="LOGO POLENN 3cm.jpg"></a>
<p><font size=2 color=#5291ef face="Calibri"><i> </i></font>
<p><font size=2 color=#5291ef face="Calibri"><i> Afin de contribuer
au respect de l'environnement, merci de n'imprimer ce courriel que si nécessaire</i></font>
<p><font size=3 color=#004080 face="Calibri"> </font>
<p><font size=2 face="Calibri"><b>De :</b> PAUL COALES [</font><a href=mailto:coalespr@btinternet.com><font size=2 face="Calibri">mailto:coalespr@btinternet.com</font></a><font size=2 face="Calibri">]
<b><br>
Envoyé :</b> jeudi 17 septembre 2009 11:27<b><br>
À :</b> trnsys-users@cae.wisc.edu<b><br>
Objet :</b> [TRNSYS-users] TRNBuild / Type56: Documentation on handling
custom inputs</font>
<p><font size=3 face="Calibri"> </font>
<p>
<br>
<table>
<tr valign=top>
<td><font size=3>Can anybody point me at documentation or examples, which
show the handling of custom Inputs to Type56 in TRNBuild.<br>
<br>
I've followed 06-mulitizonebuilding.pdf. This describes how to create
a new Input field which will appear in the interface to a Type56 instance
within the Simulation Studio but it does not show how you use it for anything
within your building model once you have created it.<br>
<br>
I'm trying to connect a heat source ( from emitters of a GSHP system )
to the described building.<br>
<br>
Thanks<br>
Paul</font></table>
<p><font size=2 face="Calibri"> </font></table>
<br><tt><font size=2>_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@cae.wisc.edu<br>
</font></tt><a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"><tt><font size=2>https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</font></tt></a><tt><font size=2><br>
</font></tt>
<br>
<br><font size=2 face="sans-serif"><br>
------------------------------------------------------------------------------------------------------------<br>
Meld deg på vårt nyhetsbrev på </font><a href=www.niva.no><font size=2 face="sans-serif">www.niva.no</font></a>