<!DOCTYPE html PUBLIC "-//W3C//DTD HTML 4.01 Transitional//EN">
<html>
<head>
  <meta content="text/html;charset=ISO-8859-1" http-equiv="Content-Type">
</head>
<body bgcolor="#ffffff" text="#000000">
Senne,<br>
  Typically the way this would be accomplished is to connect the flow
from Type60's outlet to the active layer fluid inlet temperature and
mass flow rate via a pump and to turn the pump on and off based on the
control signal of a thermostat that watches the zone temperature
(Type108 would be a good choice for the thermostat model). The tank
would then be kept warm separately by some kind of heater. Type60 has a
thermostat and heater built into it if you want to use an electric or
gas element. Take a look at parameters 15 through 29. If you are
heating the tank by external means (a solar collector, a heat pump,
etc.) then Type2 is probably the correct choice but it should look at
the tank bottom temperature and the outlet temperature of the heating
device.<br>
Kind regards,<br>
 David<br>
<br>
<br>
senne plessers wrote:
<blockquote cite="mid:SNT108-W4353B733CDE13DEF73A98FFEFD0@phx.gbl"
 type="cite">
  <style>
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 10pt;
font-family:Verdana
}
  </style>Dear all,<br>
 <br>
I recently start using trnsys16, now I have to implement a house that
has <br>
an active layer in the floor and in the ceiling. To supply the heating
I added <br>
a thermal storage (type60t) that is connected to the actieve layer and
the<br>
heating in trnbuild. <br>
 <br>
Now I want to control this heating or storage tank, I want to turn off
the heating<br>
when the temperature rises above a certain value, because above this
value it is <br>
not necessary to produce heat. I thought I had to do it with type2 but
it doesn't<br>
seem to work. Is there a way to shut the heating off in these periods?
Or am I <br>
doing something wrong with my parameters and inputs? I follow this
procedure:<br>
 <br>
Upper input temperature=25<br>
Lower input temperature I connect with the temperature of a thermal zone<br>
Monitoring temperature=0<br>
Upper dead band = 5<br>
Lower dead band=0<br>
The output control function I connect with the input of the heating<br>
 <br>
 <br>
Kind Regards,<br>
 <br>
Senne<br>
  <br>
  <hr>Je hele online leven op één stek? <a moz-do-not-send="true"
 href="http://www.microsoft.com/belux/nl/windows/windowslive/default.aspx"
 target="_new">Ontdek Windows Live!</a>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
  </pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: <a class="moz-txt-link-abbreviated" href="mailto:bradley@tess-inc.com">bradley@tess-inc.com</a> 
Web Pages:  <a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>    and      <a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a>

***********************************************************************</pre>
</body>
</html>