<br><font size=3>Yeonsook</font><font size=2 face="sans-serif">,</font>
<br>
<br><font size=2 face="sans-serif">I am not sure what excactly causes your
problem, but I can give you some advise on using PID controllers in TRNSYS
simulations.</font>
<br>
<br><font size=2 face="sans-serif">1) Use the controller in mode 0 and
with a small time step.</font>
<br><font size=2 face="sans-serif">2) Leave the on/off signal (input 3)
to 1 unless you need to force the controlled equipment to be shut down
under certain conditions. The controller will still generate a control
signal of 0 if that is what the PID algorithm predicts.</font>
<br><font size=2 face="sans-serif">3) Experiment with the P, I and D coefficients
(inputs 7, 8 and 9). If you use the Proportional term only, the control
signal will often oscillate as the set point is met in one time step but
not in the next and so on.</font>
<br><font size=2 face="sans-serif">4) Be sure to have enough thermal mass
in your system (for example tanks and pipes) and a sufficiently high thermal
capacitance of your building. That way, the system will react slower to
changes in external and internal conditions, and it will be easier for
the controller to stabilize.</font>
<br>
<br><font size=2 face="sans-serif">Hope this helps.</font>
<br>
<br><font size=2 face="sans-serif">Kind regards,</font>
<br><font size=2 face="sans-serif">Knut Erik</font>
<br><font size=2 face="sans-serif"> </font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">trnsys-users-request@cae.wisc.edu</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">trnsys-users@cae.wisc.edu</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">08/07/2009 07:08 PM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">TRNSYS-users Digest, Vol 56, Issue 9</font></table>
<br>
<hr noshade>
<br>
<br><font size=2 color=#800080 face="sans-serif"><br>
----- Message from Yeonsook Heo <yeonsook@gatech.edu> on Fri, 7 Aug
2009 08:29:15 -0700 -----</font>
<table>
<tr>
<td>
<div align=right><font size=3><b>To:</b></font></div>
<td><font size=3>trnsys-users@cae.wisc.edu</font>
<tr>
<td>
<div align=right><font size=3><b>Subject:</b></font></div>
<td><font size=3>[TRNSYS-users] PID controller to modulate the opening
of a damper</font></table>
<br><font size=3>Dear TRNSYS users,</font>
<br><font size=3> </font>
<br><font size=3>I am using PID controller to modulate the damper to control
natural ventilation coming to a space through an atrium. The problem
is that control output constantly osciallates from 0 to 1, but never stabilizes
at a certain value between them. I tried to simulate with different time
steps, but the results did not change. </font>
<br><font size=3> </font>
<br><font size=3>Could you help me what possible problems and solutions
are for this matter?</font>
<br><font size=3> </font>
<br><font size=3> </font>
<br><font size=3>Thanks,</font>
<br><font size=3>Yeonsook</font>
<br><font size=3><br>
</font><tt><font size=2>_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@cae.wisc.edu<br>
</font></tt><a href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"><tt><font size=2>https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</font></tt></a><tt><font size=2><br>
</font></tt>
<br>
<br><font size=2 face="sans-serif"><br>
------------------------------------------------------------------------------------------------------------<br>
Meld deg på vårt nyhetsbrev på </font><a href=www.niva.no><font size=2 face="sans-serif">www.niva.no</font></a>