<!DOCTYPE html PUBLIC "-//W3C//DTD HTML 4.01 Transitional//EN">
<html>
<head>
  <meta content="text/html;charset=ISO-8859-1" http-equiv="Content-Type">
</head>
<body bgcolor="#ffffff" text="#000000">
<font size="-1"><font face="Helvetica, Arial, sans-serif">Arnaud,<br>
<br>
If you want to properly account for the real interactions, there are
some trnsys add-ons (such TrnFlow) which can calculate air flows.
However, if both spaces are conditioned to the same temperature, the
interaction should be small. To test the effect, just set up a coupling
airflow between the two zones (add an input airflow equal to the temp
& humidity of one zone to the other, for each zone), and just play
with the airflow rate to see what the effect is. Assume a small flow at
first, then increase up to something really high. If all the effects
are small then I'd say ignore it. If you see some effects you're
concerned about then I'd say it's worth investigating further with the
more detailed methods. Sometimes it's good to just test the boundaries
with a simple method before you spend a lot of time with a detailed
method.<br>
<br>
And yes, if you want to account for the different thermal properties of
the door, create a new wall type and make a "wall" of the door's area.<br>
<br>
-Cramer<br>
<br>
</font></font><br>
<a class="moz-txt-link-abbreviated" href="mailto:A.Thome-08@student.lboro.ac.uk">A.Thome-08@student.lboro.ac.uk</a> wrote:
<blockquote
 cite="mid:1248786032.4a6ef6703bb81@student-webmail.lboro.ac.uk"
 type="cite">
  <pre wrap="">
Dear all,

When there are two thermal zones, adjacent to each other, without any door,
just open to each other (I actually maybe should have defined it as ONE
thermal zone only, but did
not because of architectural/orientation issues), how should I represente
the interface between the two zones? For the moment I just did not
specified anything and obviously this is not correct!

Now, If you have an interface ( wall + door = 10m2) with a door (2m2)
between the two thermal zones I have to define two types of "wall", one
which is "door type" (2m2) and the second one which is "internal adjacent"
wall type(8m2)?

Thank you for all the advices!

Arnaud.
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>


  </pre>
</blockquote>
<br>
<div class="moz-signature">-- <br>
<title></title>
<b><font face="Arial" size="1">J. Cramer Silkworth<br>
Transsolar Climate Engineering<br>
Technical consulting for energy efficiency and environmental quality in
buildings.<br>
134 Spring Street, Suite 601<br>
New York, NY 10012<br>
212-219-2255<br>
<a href="mailto:silkworth@transsolar.com"
 title="mailto:silkworth@transsolar.com">silkworth@transsolar.com</a>
</font></b></div>
</body>
</html>