Mattieu,<br>
  I think that the wall type manager is where the incorrect units are
displayed. My understanding is that a coldbridge does not have any
thickness but it does have a length. For example, if you want to make a
coldbridge to represent the lack of insulation where two exterior walls
are joined, you would define a coldbridge that has the length of the
joint. The resistance you enter should be in kJ/h.m.K (where the length
is the length of the bridge). The error in TRNBuild is that the wall
type manager should change the units of u-value when a coldbridge wall
is displayed. Note that since the u-value displayed in the wall type
manager is not actually used in calculation, that this error should not
affect your results.<br>
Kind regards,<br>
 David<br>
<br>
<br>
matthieu duclos wrote:
<blockquote
 cite="mid:17932260.105838.1239873486754.JavaMail.www@wwinf8203"
 type="cite">Dear Trnsys Users,
  <br>
  <br>
I have a problem about a bug for thermal bridge, I find an answer in
the archives but ...:
  <br>
  <br>
  <br>
Hi Nicola,
  <br>
  <br>
nicola wrote:
  <br>
> Dear all,
  <br>
> I'm modelling a wall wit a thermal bridge effect.
  <br>
> I found a bug in TRNBuilt :
  <br>
> 1. If I put the value of resistence equal to xxx (hmK/kJ) in the
layer <br>
> manager, the program create a wall with a U-value expressed in
kJ/h <br>
> m^2K and a resistence equal to xxx in hm^2k/kJ!!!
  <br>
Thanks for finding this bug. I think it is only a problem of displaying
  <br>
the units. The resistance should be entered in h m^2K /kJ, and not h m <br>
K /kJ. When you check on the 'Layer type manager', the resistance is <br>
shown in h m^2K /kJ.
  <br>
> 2. the u-value of a wall with thermal bridge effect is lower than
the <br>
> same wall without thermal bridge effect.
  <br>
The u-value displayed in the 'Wall type manager' is calculated by
adding <br>
two reference heat transfer coefficients to the wall (7.7 and 25 W/m^2
K).
  <br>
  <br>
Best regards,
  <br>
  <br>
Diego
  <br>
  <br>
  <br>
... in "Walls" when I choose a coldbridge I can put the value for
length in m , not a surface in m^2.
  <br>
  <br>
What is the solution? <br>
If the solution is all in m^2, how can I change a linear thermal bridge
to surface thermal bridge?
  <br>
  <br>
Thanks in advance,
  <br>
  <br>
Matt
  <br>
  <br>
  <br>
  <i><a moz-do-not-send="true"
 style="color: rgb(0, 0, 255); text-decoration: underline;"
 target="_blank" href="http://www.laposte.net">Créez votre adresse</a>
électronique <a class="moz-txt-link-abbreviated" href="mailto:prenom.nom@laposte.net">prenom.nom@laposte.net</a><br>
1 Go d'espace de stockage, anti-spam et anti-virus intégrés.</i><br>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
  </pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: <a class="moz-txt-link-abbreviated" href="mailto:bradley@tess-inc.com">bradley@tess-inc.com</a> 
Web Pages:  <a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>    and      <a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a>

***********************************************************************</pre>
</body>
</html>