Frédéry,<br>
 the TrnsysConstants file is in the ..\Trnsys16\SourceCode\Kernel
directory. The process for recompiling the DLL depends on which
compiler you are using. The two most likely are the Compaq Visual
Fortran compiler or the Intel Visual Fortran compiler. If you do not
have a Fortran compiler then you will need to ask your distributor to
create a TRNDll.dll with a higher limit on the number of equations for
you.<br>
Kind regards,<br>
 David<br>
<br>
<br>
frédéry lavoye wrote:
<blockquote
 cite="mid:a88a8f180903200417jb346776l836c0125d2658f91@mail.gmail.com"
 type="cite">Dear trnsys users,<br>
I'm simulating an energetic concept on trnsys simulation studio and
i've this error message:<br>
"TRNSYS message 14; the trnsys processor has reported an error while
trying to process EQUATIONS and CONSTANTS in the provided TRNSYS input
file. The maximum allowable number of constants + equations has been
exceeded. Either reduce the number of equations and constants in the
input file or increase the limit on the number of equations and
constants. If the limit is to be increased, the variable nMaxEquations
should be modified in the TrnsysConstants file. The TRNSYS source code
will then have to be re-compiled and a new TRNSYS dynamic link librairy
created."<br>
  <br>
I cannot reduce the number of equations and constants otherwise my
model is false. How can i re-compiled my TRNSYS source code and is
there any risk in doing that ? Furthermore, where can i find the
Trnsysconstants file ?<br>
Thanks for your answer.<br>
Best Regards.<br>
Frédéry.<br>
  <br>
  <div class="gmail_quote">2009/3/19 <span dir="ltr"><<a
 moz-do-not-send="true" href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br>
  <blockquote class="gmail_quote"
 style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">Send
TRNSYS-users mailing list submissions to<br>
       <a moz-do-not-send="true" href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
    <br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
       <a moz-do-not-send="true"
 href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
 target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>
       <a moz-do-not-send="true"
 href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
    <br>
You can reach the person managing the list at<br>
       <a moz-do-not-send="true"
 href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
    <br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of TRNSYS-users digest..."<br>
    <br>
Today's Topics:<br>
    <br>
  1. Runtime error using Type155 Matlab Calling (Giacomo Barale)<br>
  2. Re: (no subject) (David Bradley)<br>
    <br>
    <br>
---------- Message transféré ----------<br>
From: "Giacomo Barale" <<a moz-do-not-send="true"
 href="mailto:stage02@ferasrl.it">stage02@ferasrl.it</a>><br>
To: <<a moz-do-not-send="true"
 href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>
Date: Thu, 19 Mar 2009 10:34:41 +0100<br>
Subject: [TRNSYS-users] Runtime error using Type155 Matlab Calling<br>
    <div>
    <div><font face="Arial" size="2"><span>Dear all,</span></font></div>
    <div><font face="Arial" size="2"><span></span></font> </div>
    <div><font face="Arial" size="2"><span>I wrote some some small
programs in matlab using .m files. I then coupled these .m files with
Trnsys16 Studio using the type155 component. They work fine
individually, but when i try to make them comunicate, linking outputs
from one of them to inputs of another one, i receive this error message:</span></font></div>
    <div><font face="Arial" size="2"><span></span></font> </div>
    <div><font face="Arial" size="2"><span>"Runtime error!</span></font></div>
    <div><font face="Arial" size="2"><span></span></font> </div>
    <div><font face="Arial" size="2"><span>Program: C:\Program
Files\Trnsys16\Exe\TRNExe.exe</span></font></div>
    <div><font face="Arial" size="2"><span></span></font> </div>
    <div><font face="Arial" size="2"><span>This application has
requested the Runtime to terminate it in an unusual way."</span></font></div>
    <div><font face="Arial" size="2"><span></span></font> </div>
    <div><font face="Arial" size="2"><span>On the other end,
liniking the Type155 with a different component, as the weather data
reading and processing Type109, doesn't give me the same problem.</span></font></div>
    <div><font face="Arial" size="2"><span></span></font> </div>
    <div><font face="Arial" size="2"><span></span></font> </div>
    <div><font face="Arial" size="2"><span></span></font> </div>
    <div><font face="Arial" size="2"><span>Can anyone help me to solve
this problem?</span></font></div>
    <div><font face="Arial" size="2"><span></span></font> </div>
    <div><font face="Arial" size="2"><span>Thank a lot in advance</span></font></div>
    <div><font face="Arial" size="2"><span></span></font><font
 face="Arial" size="2"><span>Best regards</span></font></div>
    <div><font face="Arial" size="2"><span></span></font> </div>
    <div><font face="Arial" size="2"><span>Giacomo</span></font></div>
    </div>
    <br>
    <br>
---------- Message transféré ----------<br>
From: David Bradley <<a moz-do-not-send="true"
 href="mailto:bradley@tess-inc.com">bradley@tess-inc.com</a>><br>
To: Giorgos Fragogiannis <<a moz-do-not-send="true"
 href="mailto:gfrago@metal.ntua.gr">gfrago@metal.ntua.gr</a>><br>
Date: Thu, 19 Mar 2009 11:20:21 -0500<br>
Subject: Re: [TRNSYS-users] (no subject)<br>
    <div bgcolor="#ffffff" text="#000000">Giorgos,<br>
  I would stay with Type753 (heating coil) and Type508 (cooling coil)
if indeed that is how the building is being heated and cooled. I am not
sure how you are controlling the system but I would recommend putting
the zones into temperature level control and adding a thermostat that
turns on and off the flow to each coil depending on the temperature of
the zone (instead of calculating a zone load and then somehow imposing
that on the coils. You may also need to use some diverting valves
(Type11) to control whether the water from your heat pump is going to
the heating or the cooling coil.<br>
Kind regards,<br>
 David<br>
    <br>
    <br>
Giorgos Fragogiannis wrote:
    <blockquote type="cite">
      <div>
      <p><span lang="EN-US">Dear all</span></p>
      <p><span lang="EN-US">I am new user in trnsys and I
try to
simulate o ground source heat pump system connected to o 7 zone
building (type
56), in order to study the interrelation between  ground, HP (water to
water), fan coil and building. </span></p>
      <p><span lang="EN-US">My question is what type of
fan coil I must
used in order to meet  the  heating and cooling demand?</span></p>
      <p><span lang="EN-US">Until now I tried  to solve
this
problem by using type 753 and 508 simultaneously, but it is difficult
to controlled
it!</span></p>
      <p><span lang="EN-US"> </span></p>
      <p><span lang="EN-US">Is the right way to use of
water to air
heat pump (type 505), as fan coil  or you have any other idea about
this
problem ?</span></p>
      <p><span lang="EN-US"> </span></p>
      <p><span lang="EN-US">My Regards </span></p>
      <p><span lang="EN-US"> George Fragogiannis</span></p>
      <p><span lang="EN-US">National Technical University
of Athens</span></p>
      <p><span lang="EN-US">School of Mining and
Metallurgical
Engineering</span></p>
      </div>
      <pre><hr size="4" width="90%">
_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu"
 target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true"
 href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
 target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
  </pre>
    </blockquote>
    <br>
    <pre cols="72">-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: <a moz-do-not-send="true" href="mailto:bradley@tess-inc.com"
 target="_blank">bradley@tess-inc.com</a> 
Web Pages:  <a moz-do-not-send="true" href="http://www.tess-inc.com"
 target="_blank">http://www.tess-inc.com</a>    and      <a
 moz-do-not-send="true" href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a>

***********************************************************************</pre>
    </div>
    <br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
    <a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
    <a moz-do-not-send="true"
 href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users"
 target="_blank">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a><br>
    <br>
  </blockquote>
  </div>
  <br>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
  </pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: <a class="moz-txt-link-abbreviated" href="mailto:bradley@tess-inc.com">bradley@tess-inc.com</a> 
Web Pages:  <a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>    and      <a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a>

***********************************************************************</pre>
</body>
</html>