Rahma,<br>
The TRNSYS result (*.lst and *.log) files should show you more
information on the cause of the error. However, if I had to guess about
it, I would first check and make sure that the mass flow rate that goes
to your active layer (as an input to Type56) is always either 0 or
about 10% above the 750 kg/h that TRNBuild calculates as the required
minimum value. The additional 10% is a bit of a mystery to me. I have
run across it quite a few times and I think it might have something to
do with issues of the density of the active layer liquid changing with
temperature. If keeping the flow rate higher does not work then in your
active layer specification, try setting the "minimum desired inlet mass
flow rate" to 10 (the default) instead of 5 and again make sure that
whenever there is flow going to though the floor, it is above 1500 kg/h.<br>
Kind regards,<br>
David<br>
<br>
Rahma GUECHCHATI wrote:
<blockquote
cite="mid:58b6d8d80806131141y13b42b48p82126b19cef73df4@mail.gmail.com"
type="cite">
<p class="MsoNormal" style="margin: 0cm 0cm 0pt;"><span style=""
lang="EN-GB"><font size="4"><font face="times new roman,serif">Hello;</font></font></span></p>
<p class="MsoNormal" style="margin: 0cm 0cm 0pt;"><span style=""
lang="EN-GB"><font size="4"><font face="times new roman,serif"> </font></font></span></p>
<p class="MsoNormal" style="margin: 0cm 0cm 0pt;"><span style=""
lang="EN-GB"><font size="4"><font face="times new roman,serif">I want
simulate a building (type 56) heated by a direct solar floor used
active layer defined in TRNBuild.</font></font></span></p>
<p class="MsoNormal" style="margin: 0cm 0cm 0pt;"><span style=""
lang="EN-GB"><font size="4"><font face="times new roman,serif">I
created a wall with an active layer After finishing the wall
definition, the wall is marked with an "A" in the overview box of walls.</font></font></span></p>
<div class="MsoNormal" style="margin: 0cm 0cm 0pt;"><span style=""
lang="EN-GB"><font face="times new roman,serif" size="4">then I click
on Active Layer Specification Bar, i defined all the parameters "inlet
temperature=1*tfluid, number of fluid loops=50, inlet mass flow
rate=1*flow rate,gain=0" then i pushing the DO-Button but the wall
window shows the active layer wall i defined does not indicated by AS.
it is always defined by A and when I run my project I get error. I want
to know where is the problem.</font></span></div>
<div class="MsoNormal" style="margin: 0cm 0cm 0pt;"><span style=""
lang="EN-GB"><font size="4"><font face="times new roman,serif"> </font></font></span></div>
<div class="MsoNormal" style="margin: 0cm 0cm 0pt;"><span style=""
lang="EN-GB"><font face="times new roman,serif" size="4">Best regard</font></span></div>
<div class="MsoNormal" style="margin: 0cm 0cm 0pt;"><span style=""
lang="EN-GB"></span> </div>
<p class="MsoNormal" style="margin: 0cm 0cm 0pt;"><span style=""
lang="EN-GB"><font size="4"><font face="times new roman,serif">rahma</font></font></span></p>
<pre wrap="">
<hr size="4" width="90%">
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@engr.wisc.edu">TRNSYS-users@engr.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: <a class="moz-txt-link-abbreviated" href="mailto:bradley@tess-inc.com">bradley@tess-inc.com</a>
Web Pages: <a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a> and <a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a>
***********************************************************************</pre>