<div>Dear Boris,</div>
<div> I think that naming your *.bui file something other than the name of your *.tpf and *.dck, will solve the problem. When TRNEdit runs a parametric table, it automatically reproduces all files that have the same name as the input file, appending the run number onto the name. Because your input file is called MyProject.dck and your building description is called MyProject.bui, TRNEdit is trying to duplicate both. Try naming your building something like Building.bui.</div>
<div> Kind regards,</div>
<div> David</div>
<div>
<br>
<br>
<br>
<br>
Technical Support Team<br>Thermal Energy System Specialists, LLC<br>2916 Marketplace Dr, Suite 104<br>Madison, WI 53719<br>techsupport@tess-inc.com
<br>
<br>----- Original Message -----
<br>
Subject: [TRNSYS-users] parametric runs with type 56
<br>
From: boris.perrin@fr.schneider-electric.com
<br>
Date: Wed, April 30, 2008 5:06
<br>
<table><tbody><tr><td width="1" bgcolor="#f1c352">
<br></td><td valign="top">
<div class="PrivateMsgDiv"><!-- begin sanitized html -->
<br><font size="2" face="sans-serif">Dear All, </font>
<br>
<br><font size="2" face="sans-serif">I'm working on a parametric study, using
a type 56. I created a project MyProject.tpf, using the multizone building
wizard.</font>
<br>
<br><font size="2" face="sans-serif">My variable is the set temperature,
which I define as an input in TRNBuild. </font>
<br>
<br><font size="2" face="sans-serif">I specify that this input should be
handled as a "constant", so I get this variable available in
the parametric table, using TRNEdit.</font>
<br>
<br><font size="2" face="sans-serif">The output file of my type 25 is "***.out",
so that TRNEdit appends the run number to the output files.</font>
<br>
<br><font size="2" face="sans-serif">But when I come to runing the table,
I have an error message from TRNBuild. In fact, it creates a file "MyProject1.bui",
which is empty. </font>
<br><font size="2" face="sans-serif">Indeed, it seems that it creates an
empty ".bui" file, instead of copying the data from the
file " MyProject.bui".</font>
<br>
<br><font size="2" face="sans-serif">I can solve this problem by copying
the file MyProject.bui and renaming it into MyProject1.bui, MyProject2.bui,
MyProject3.bui, which is not very convenient.</font>
<br>
<br><font size="2" face="sans-serif">Do you have any idea on how to proceed
to get "MyProject1.bui", "MyProject2.bui", "MyProject3.bui"...
with the same data as in the original " MyProject.bui"?</font>
<br>
<br><font size="2" face="sans-serif">Or maybe the solution is to specify
that it has to use "MyProject.bui" for each parametric run? In
that case, any idea on how to proceed?</font>
<br>
<br><font size="2" face="sans-serif">Thanks a lot if you can help me solving
this problem.</font>
<br>
<br><font size="2" face="sans-serif">Best regards</font>
<br>
<br><font size="2" face="sans-serif">Boris</font>
<br><!-- end sanitized html -->
<hr size="1" noshade="noshade">
<pre>_______________________________________________<br>TRNSYS-users mailing list<br><a href="javascript:bodyCreateMail('TRNSYS-users%40engr.wisc.edu')">TRNSYS-users@engr.wisc.edu</a>
<br><a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></pre></div></td></tr></tbody></table></div>