<div>Since the plugin is programmed with the American standard of denoting numbers, you will need the data file to use periods for decimal points.</div>
<div> </div>
<div>Also, the plugin is not expecting to see the comments in the file and will error out on trying to read the data file with the comments.</div>
<div> </div>
<div>Regards,</div>
<div> </div>
<div>Tim</div>
<div>
<br>
<br>
<br>
<br>----------------------------------
<br>Timothy McDowell
<br>Executive Vice President
<br>Thermal Energy System Specialists, LLC
<br>2916 Marketplace Dr, Suite 104
<br>Madison, WI 53719
<br>Phone: 608-274-2577
<br>Fax: 608-278-1475
<br>
<br>----- Original Message -----
<br>Subject: [TRNSYS-users] Plugin Tess Type 534
<br>From: "Jens Apel" <jens_apel@arcor.de>
<br>Date: Tue, October 30, 2007 10:05
<br></div>
<table>
<tbody>
<tr>
<td width="1" bgcolor="#a2b6d2"> </td>
<td valign="top">
<div class="PrivateMsgDiv"><!-- begin sanitized html -->
<style></style>
<div class="bodyclass">
<div class="Section1">
<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">Dear all,</span></font></p>
<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>
<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;" lang="EN-GB">I'm, using TRNSYS 16.1 with TESS libs 2.0 V1 with the simulation studio. When I configure the tank type 534 with the plugin I get the following problems. I have a tank volume of 1.83 cubic metres and a tank height of 2.69 metres and put it in exactly like that. When I then close the plugin and open the tank input file *.dat there are the correct values, but with a comma "," instead of a dot ".". So the next time I open the plugin I have got a tank volume of 1 cubic metre, a height of 83 metres and propylene glycol -- water mixture with 69 percent. So the tank takes the parameters comma separated.</span></font></p>
<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;" lang="EN-GB">Did anybody come along the same problem and knows advice? Is it possible that it is because I'm running a german operating system where the dot "." is changed to a comma ","? Can I write comments into the tank input file? I tried "*" and "!" but seemingly that didn't work.</span></font></p>
<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;" lang="EN-GB">Thanks for any help</span></font></p>
<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;" lang="EN-GB">Jens Apel</span></font></p>
<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;" lang="EN-GB">Technical University of Berlin</span></font></p></div></div><!-- end sanitized html -->
<hr noshade="noshade" size="1">
<pre>_______________________________________________
TRNSYS-users mailing list
<a href="javascript:bodyCreateMail('TRNSYS-users@engr.wisc.edu')">TRNSYS-users@engr.wisc.edu</a>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" target="_blank">https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
</pre></div></td></tr></tbody></table>