<html>
<body>
Mattheiu,<br>
  I have not run into that error but I would guess that it means
that the air flow from zone A to zone B was calculated as a negative
number. Airflow from zone A to zone B must always be positive. If the air
flow turns around and flows the other direction then you need to define a
coupling air flow rate from zone B to zone A. The reason for this is that
by defining only positive air flows (perhaps in both directions) you can
define a mixing flow, not just a net flow between the two zones.<br>
Cheers, <br>
David<br><br>
<br>
At 09:52 6/20/2007, Matthieu Cosnier wrote:<br>
<blockquote type=cite class=cite cite="">Dear TRNSYS users<br>
Does anybody know what  the error message "negative coupling
value" mean? <br>
It seems to be due to type 56. <br>
My simulation program works usualy but not for a particular ventilation
air flow rate.<br>
Thanks for your answers<br><br>
COSNIER Matthieu <br><br>
<font size=2>
*************************************************************<br>
Doctorant<br>
LOCIE<br>
Polytech'Savoie - Université de Savoie<br>
Campus Scientifique Savoie Technolac <br>
73376 Le bourget du lac Cedex (FRANCE)<br>
Tel : +33(0)4 79 75 88 21  poste(77 69)<br>
email:
</font><font size=2 color="#0000FF"><u>
matthieu.cosnier@etu.univ-savoie.fr<br>
</u></font><font size=2>
*************************************************************<br><br>
</font>_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@engr.wisc.edu<br>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" eudora="autourl">
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></blockquote>
<x-sigsep><p></x-sigsep>
****************************************************************************************<br>
Thermal Energy System Specialists (TESS), LLC <br>
David
BRADLEY                          
2916 Marketplace Drive - Suite 104 <br>
Partner                                       
Madison, WI 53719 <br>
Phone: (608) 274-2577 USA <br>
Fax: (608) 278-1475 <br>
E-mail: bradley@tess-inc.com <br>
Web Pages: 
<a href="http://www.tess-inc.com/" eudora="autourl">
http://www.tess-inc.com</a>    
and     
<a href="http://www.trnsys.com/" eudora="autourl">
http://www.trnsys.com<br><br>
</a>"Providing software solutions for today's energy engineering
projects" <br>
****************************************************************************************<br>
</body>
</html>