Steve,<br>
If you are reading a standard TMY file (either TMY, TMY2, or the
old TRNSYS TMY format), I would suggest that you replace Type9 with
Type15. Type15 combines the functionality of Type89 (which reads standard
format files such as TMY2 and TRNSYS TMY) with Type16 and Type69. It
avoids some of the problems of setting Type16 parameters correctly and of
making connections between those components. Also, be sure that you
changed the start time of your simulation. The TRNSYS 15 convention was
that the start time was the hour of the year at the end of the first time
step (although often you had to tweak this around to get it to actually
work correctly). In TRNSYS 16, the start time is the hour of the year at
the beginning of the first time step. I hope that helps.<br>
David<br><br>
<br>
At 12:20 5/28/2007, Steven Long wrote:<br>
<blockquote type=cite class=cite cite=""><font size=2>Hi:<br>
<br>
I’m converting a series of decks to TRNSYS 16. When I run the decks
using TRNSYS 16 source code with the deck version as “15” I don’t
get any radiation or data problems, beyond the warning about the new
start time convention. My results are similar to TRNSYS 15.<br>
<br>
I then converted the decks to “version 16” and made the changes to the
type 9 that are described in the user manual. I’m using TMY data
for the entire year, but I’m not using all columns of the entire TMY
file, so I’m not using the default TMY reader mode. Now when I run
these decks, I got the following results:<br>
<br>
1.</font><font face="Times New Roman, Times" size=1>
</font><font size=2>Many type 16 errors due to radiation exceeding the
SC.<br>
2.</font><font face="Times New Roman, Times" size=1>
</font><font size=2>A minimum collector temperature that is below
anything in the data file.<br>
3.</font><font face="Times New Roman, Times" size=1>
</font><font size=2>Similar overall results to TRNSYS 15.<br>
<br>
My type 9 is as follows:<br>
<br>
(Idn=input 2,ih= input 3)<br>
<br>
</font><font face="Fixedsys" size=1>UNIT 1 TYPE 9 DATA READER<br>
PARAMETERS 34<br>
3 0 7 1 <br>
1 1 0 0<br>
-2 1 0 0<br>
-3 1 0 0<br>
4 1 0 0<br>
5 1 0 0<br>
6 1 0 0<br>
7 1 0 0<br>
10 -1<br>
<br>
I have tried various modes and get similar errors. If I add one
“starter” line to the TMY file and change to mode 5/6, I get fewer
radiation errors.<br>
<br>
I also looked at type 16 and it appeared that this changed as well:<br>
<br>
UNIT 66 TYPE 16 RADIATION PROCESSOR<br>
PARAMETERS 9<br>
* RADMODE TRACKMODE TILTMODE
DAY
LAT
SC
SHFT SMOOTH<br>
4
1
2 ZSTARTDAX1 GLATITUDC1
XSOLARCOC1 ZSHIFTLOC1 2<br>
* IE<br>
-1<br>
INPUTS 7<br>
* I
IDN
TD1
TD2
RHOG
BETAI GAMMAI<br>
1,3 1,2 1,99 1,100 0,0
0,0 0,0<br>
0
0
0
0 ZGROUNDRC1
GCOLSLOPC1 GCOLAZIMC1<br>
<br>
</font><font size=2>It appears that the smooth mode is no longer used and
the last parameter should be -1. Looking at the documentation, it
was unclear what inputs 3 and 4 should be as they are listed as 19,20 in
type 16, but the older convention of 99,100 is still indicated in the
type 9 documentation.<br>
<br>
Do you have any ideas as to what I may be doing wrong?<br>
<br>
Thanks,<br>
<br>
<br>
Steven Long<br>
</font>_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@engr.wisc.edu<br>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" eudora="autourl">
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></blockquote>
<x-sigsep><p></x-sigsep>
****************************************************************************************<br>
Thermal Energy System Specialists (TESS), LLC <br>
David
BRADLEY
2916 Marketplace Drive - Suite 104 <br>
Partner
Madison, WI 53719 <br>
Phone: (608) 274-2577 USA <br>
Fax: (608) 278-1475 <br>
E-mail: bradley@tess-inc.com <br>
Web Pages:
<a href="http://www.tess-inc.com/" eudora="autourl">
http://www.tess-inc.com</a>
and
<a href="http://www.trnsys.com/" eudora="autourl">
http://www.trnsys.com<br><br>
</a>"Providing software solutions for today's energy engineering
projects" <br>
****************************************************************************************<br>
</body>
</html>