Vincent,<br>
 I am not sure whether anyone responded to you about this but my
understanding is that Type56 does not perform any air pressure checks. It
assumes that whatever air you put into a zone, gets out of that zone. If
you have a particular ventilation system setup in which you supply air to
one zone and it returns from another then you need to specify a mass flow
rate of air (equal to the mass flow rate that you supplied) that
transfers from the supply zone to the return zone through an opening in
an ADJACENT wall. TRNFlow, COMIS, or CONTAM (Type97) can be used to
calculate such interzonal flow rates if they are not simple.<br><br>
 The way we ususally "extract" air from a zone is to
supply air to that zone through three Type56 inputs (T_VENT, RH_VENT,
ACH_VENT). We then take the Type56 outputs for zone temperature and
relative humidity and the outlet flow rate from the supply fan (which
passes around Type56) for the return device.<br><br>
Kind regards,<br>
 David<br><br>
<br><br>
At 08:06 5/24/2007, PARTENAY, Vincent wrote:<br>
<blockquote type=cite class=cite cite=""><font size=2>Hello Trnsys
users,<br>
 <br>
I’m simulating a mutizone building in Trnbuild and I don’t understand how
air coupling flows, ventilation and infiltration are balanced (in order
not to overload the building for example). How can I extract air from the
building ?<br>
 <br>
Thanks in advance,<br>
 <br>
Vincent Partenay<br>
</font><br><br>
<br><br>
************************************************************************************<br>
This footnote confirms that this email message has been scanned by<br>
PineApp Mail-SeCure for the presence of malicious code, vandals &
computer viruses.<br>
************************************************************************************<br>
<br>
<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@engr.wisc.edu<br>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" eudora="autourl">
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></blockquote>
<x-sigsep><p></x-sigsep>
****************************************************************************************<br>
Thermal Energy System Specialists (TESS), LLC <br>
David
BRADLEY                          
2916 Marketplace Drive - Suite 104 <br>
Partner                                       
Madison, WI 53719 <br>
Phone: (608) 274-2577 USA <br>
Fax: (608) 278-1475 <br>
E-mail: bradley@tess-inc.com <br>
Web Pages: 
<a href="http://www.tess-inc.com/" eudora="autourl">
http://www.tess-inc.com</a>    
and     
<a href="http://www.trnsys.com/" eudora="autourl">
http://www.trnsys.com<br><br>
</a>"Providing software solutions for today's energy engineering
projects" <br>
****************************************************************************************<br>
</body>
</html>