<html>
<body>
Samir,<br>
 The error is because your entering dry bulb temperature (connected
from Type109 ambient temperature) is less than your entering wet bulb
temperature (set to a constant value of 22C) at time 1 of your
simulation. Since wet bulb temperature is not a direct output of Type109,
you need to connect both dry and wet bulb temperature from the component
labeled "psychrometrics" to the cooling coil.<br>
Cheers,<br>
 David<br><br>
<br>
At 06:30 5/15/2007, Chehal, Samir wrote:<br><br>
<blockquote type=cite class=cite cite=""><font size=2>Dear Trnsys
users,<br>
</font><br>
<font size=2>I have a problem with my</font>
<font size=2>connection:</font> <font size=2>input 1 of</font>
<font size=2>“Batt froide CTA hbgt so” is not correct and I don’t know
why.<br>
</font><br>
<font size=2>The message error is:<br>
</font><br>
<font face="Courier New, Courier" size=2>*** Fatal Error at
time   :        
1.000000<br>
</font><br>
<font face="Courier New, Courier" size=2>    Generated by
Unit     :    17<br>
</font><br>
<font face="Courier New, Courier" size=2>    Generated by
Type     :    32<br>
</font><br>
<font face="Courier New, Courier" size=2>    TRNSYS
Message    103 : The TRNSYS TYPE checking routine has
found an inconsistency in the specified component between the input file
and the information expected by the Type<br>
</font><br>
<font face="Courier New, Courier" size=2>    Reported
information  : An illegal INPUT value has been reported by the
model. The model has reported that Input 1 is the problem - but this may
not be the case. Please check the component configuration.<br>
</font><br>
<font size=2><<Wizard25.tpf>> <br>
</font><br>
<font face="Courier New, Courier" size=2>Best Regards<br>
</font>=========================================================<br><br>
NOTICE - This communication may contain confidential and privileged <br>
information that is for the sole use of the intended recipient. Any
viewing,<br>
copying or distribution of, or reliance on this message by
unintended<br>
recipients is strictly prohibited. If you have received this message
in<br>
error, please notify us immediately by replying to the message and
deleting<br>
it from your computer.<br><br>
========================================================= <br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@engr.wisc.edu<br>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" eudora="autourl">
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></blockquote>
<x-sigsep><p></x-sigsep>
****************************************************************************************<br>
Thermal Energy System Specialists (TESS), LLC <br>
David
BRADLEY                          
2916 Marketplace Drive - Suite 104 <br>
Partner                                       
Madison, WI 53719 <br>
Phone: (608) 274-2577 USA <br>
Fax: (608) 278-1475 <br>
E-mail: bradley@tess-inc.com <br>
Web Pages: 
<a href="http://www.tess-inc.com/" eudora="autourl">
http://www.tess-inc.com</a>    
and     
<a href="http://www.trnsys.com/" eudora="autourl">
http://www.trnsys.com<br><br>
</a>"Providing software solutions for today's energy engineering
projects" <br>
****************************************************************************************<br>
</body>
</html>