Betrand,<br>
I think you are going to need to use two controllers. The first
controller will determine the flow rate of your collector loop in order
to maintain a collector outlet temperature of 70C. The other controller
will determine the flow rate on the load side of your heat exchanger in
order to maintain source side outlet temperature of 60C. I am also not
sure that Type2 is an appropriate controller model; Type2 models a
differential controller that has only two states: ON and OFF. In order to
modulate your flow and maintain an outlet temperature, you will need to
use a proportional or a PID controller. There are some solar collector
models in the TESS Solar Library that combine a variable speed pump,
controller, and collector and modulate the required inlet flow rate in
order to maintain an outlet temperature. <br>
Kind regards,<br>
David<br><br>
<br>
At 01:50 5/10/2007, tchanche fankam bertrand wrote:<br>
<blockquote type=cite class=cite cite="">Dear all,<br>
i am simulating a system that comprises a subsystem made of a colector
loop(ETC collector, pump, flat plate heat exchanger ). i need to to keep
the inlet temperature of the collector at 60C and the outlet temperature
at 70C. <br>
I would like to know if it is possible to control the system with type 2
and how.<br>
Thank in advance for your help.<br>
yours,<br><br>
<br>
------------------------<br>
TCHANCHE FANKAM Bertrand<br><br>
C/O SUH Christopher<br>
22 kadmeas-BOTANIKOS<br>
11855 Athens, GREECE<br>
mobile:+30 694 295 5952<br>
office: +30 210 529 4046<br><br>
<br>
Découvrez une nouvelle façon d'obtenir des réponses à toutes vos
questions ! Profitez des connaissances, des opinions et des expériences
des internautes sur
<a href="http://fr.rd.yahoo.com/evt=42054/*http://fr.answers.yahoo.com">
Yahoo! Questions/Réponses</a>. <br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@engr.wisc.edu<br>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" eudora="autourl">
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></blockquote>
<x-sigsep><p></x-sigsep>
****************************************************************************************<br>
Thermal Energy System Specialists (TESS), LLC <br>
David
BRADLEY
2916 Marketplace Drive - Suite 104 <br>
Partner
Madison, WI 53719 <br>
Phone: (608) 274-2577 USA <br>
Fax: (608) 278-1475 <br>
E-mail: bradley@tess-inc.com <br>
Web Pages:
<a href="http://www.tess-inc.com/" eudora="autourl">
http://www.tess-inc.com</a>
and
<a href="http://www.trnsys.com/" eudora="autourl">
http://www.trnsys.com<br><br>
</a>"Providing software solutions for today's energy engineering
projects" <br>
****************************************************************************************<br>
</body>
</html>