Stephan,<br>
  Our lives would be so much easier if architects would just make
square buildings, wouldn't they? :-) When faced with similar problems, I
used TNO's CpGenerator but broke the building up into rectangular
sections, treating the other sections as obstructions. I think you will
have to do your building in five sections as follows (in each top view,
the modeled rectangular section is in red and everything in black is
treated as an obstruction.<br><br>
<font face="Courier New, Courier" color="#FF0000">22222222222222</font>
<font face="Courier New, Courier">00022222222222222<br>
0000000000000000000000000000000<br>
0000000000000000000000000000000<br>
0000000000000000000000000000000<br>
5555555555550000000555555555555<br><br>
22222222222222000</font><font face="Courier New, Courier" color="#FF0000">
22222222222222<br>
</font><font face="Courier New, Courier">
0000000000000000000000000000000<br>
0000000000000000000000000000000<br>
0000000000000000000000000000000<br>
5555555555550000000555555555555<br><br>
2222222222222200022222222222222<br>
</font><font face="Courier New, Courier" color="#FF0000">
0000000000000000000000000000000<br>
0000000000000000000000000000000<br>
0000000000000000000000000000000<br>
</font><font face="Courier New, Courier">
5555555555550000000555555555555<br><br>
2222222222222200022222222222222<br>
0000000000000000000000000000000<br>
0000000000000000000000000000000<br>
0000000000000000000000000000000<br>
</font><font face="Courier New, Courier" color="#FF0000">
555555555555</font><font face="Courier New, Courier">
0000000555555555555<br><br>
2222222222222200022222222222222<br>
0000000000000000000000000000000<br>
0000000000000000000000000000000<br>
0000000000000000000000000000000<br>
5555555555550000000</font>
<font face="Courier New, Courier" color="#FF0000">555555555555<br><br>
</font>Cheers,<br>
 David<br><br>
<br>
At 04:58 4/19/2007, Stefan de Kool wrote:<br>
<blockquote type=cite class=cite cite=""><font size=2>Dear All,<br>
 <br>
I am looking for a programm to calculate Cp-values on a building facade.
I know of CP-CALC+ and TNO’s CP-gen, but both only consider rectangular
shaped buildings. The building I have looks like this in cross
section:<br>
</font><font face="Courier New, Courier" size=2> <br>
</font>Cross section:<br>
<font face="Courier New, Courier" size=2> <br>
level<br>
  5     xx<br>
  4     xx <br>
  3     xx<br>
  2     xx    xx<br>
  1     xx    xx<br>
  0     xxxxxxxx<br>
</font> <br>
Top view:<br>
<b> <br>
<font face="Courier New, Courier" size=2>22222222222222</b></font>
<font face="Courier New, Courier">000<b>22222222222222<br>
</b></font><font face="Courier New, Courier" size=2>
0000000000000000000000000000000<br>
0000000000000000000000000000000<br>
0000000000000000000000000000000<br>
<b>555555555555</b></font><font face="Courier New, Courier">0000000<b>
555555555555<br>
</b></font><font size=2> <br>
Level 0 is a carparking, levels 1-5 are dwellings. <br>
I want to estimate cp-values at the roof of level 0 as some ventilation
openings might be situated here. I am interessed in the flow to/from
these openings.<br>
 <br>
Does anyone have any suggestions?<br>
 <br>
Met vriendelijke groeten,<br>
Stefan de Kool<br>
</font><font face="Times New Roman, Times"> <br>
</font><font size=2 color="#000080">Cauberg-Huygen Raadgevende Ingenieurs
B.V.<br>
Bezoekadres: Boterdiep 48, 3077 AW  ROTTERDAM<br>
Postadres: Postbus 9222, 3007 AE  ROTTERDAM<br>
Telefoon: +31 (0)10-2443638<br>
Fax: +31 (0)10-425 44 43<br>
<a href="http://www.chri.nl/" eudora="autourl">http://www.chri.nl</a><br>
E-mail: s.dekool@chri.nl<br>
 <br>
</font>
<img src="cid:7.1.0.9.0.20070419093235.02bca9c0@tess-inc.com.1" width=300 height=75 alt="[]">
<br>
<font size=2 color="#000080"> <br>
</font><font size=2> <br>
 <br>
</font><br><br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@engr.wisc.edu<br>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" eudora="autourl">
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></blockquote>
<x-sigsep><p></x-sigsep>
****************************************************************************************<br>
Thermal Energy System Specialists (TESS), LLC <br>
David
BRADLEY                          
2916 Marketplace Drive - Suite 104 <br>
Partner                                       
Madison, WI 53719 <br>
Phone: (608) 274-2577 USA <br>
Fax: (608) 278-1475 <br>
E-mail: bradley@tess-inc.com <br>
Web Pages: 
<a href="http://www.tess-inc.com/" eudora="autourl">
http://www.tess-inc.com</a>    
and     
<a href="http://www.trnsys.com/" eudora="autourl">
http://www.trnsys.com<br><br>
</a>"Providing software solutions for today's energy engineering
projects" <br>
****************************************************************************************<br>
</body>
</html>