I think that you can handle the damper using Type11 as a controlled
damper. Take the mass flow rate of air that is coming out of the thermal
storage wall as an OUTPUT and pass it as the INPUT mass flow rate of air
into Type11. Type11 will then have two outlet air streams. One of those
outlet streams will go to your building model while the other will go to
ambient. You will then have to write an equation that determines whether
the air that is flowing into the Type11 goes to the zone or to ambient.
If you need a more detailed explanation, please let me know.<br>
Kind regards,<br>
 David<br><br>
<br>
At 07:25 9/6/2006, min wrote:<br>
<blockquote type=cite class=cite cite="">
<font face="Times New Roman, Times">hello,<br>
I simulate a thermal storage wall with TRNSYS 15. I want to know how to
manipulate the vents from day to night? In winter, the upper vent should
be closed Durant the night.<br>
Thanks<br>
<?xml:namespace prefix = o ns =
"urn:schemas-microsoft-com:office:office" /></font>
<br><br>
<br>
Nouveau : téléphonez moins cher avec Yahoo! Messenger ! Découvez les
tarifs exceptionnels pour appeler la France et l'international.
<a href="http://us.rd.yahoo.com/messenger/mail_taglines/default/*http://fr.beta.messenger.yahoo.com">
Téléchargez</a> la version beta. <br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@engr.wisc.edu<br>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" eudora="autourl">
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></blockquote>
<x-sigsep><p></x-sigsep>
****************************************************************************************<br>
Thermal Energy System Specialists (TESS), LLC <br>
David
BRADLEY                          
2916 Marketplace Drive - Suite 104 <br>
Partner                                       
Madison, WI 53719 <br>
Phone: (608) 274-2577 USA <br>
Fax: (608) 278-1475 <br>
E-mail: bradley@tess-inc.com <br>
Web Pages: 
<a href="http://www.tess-inc.com/" eudora="autourl">
http://www.tess-inc.com</a>    
and     
<a href="http://www.trnsys.com/" eudora="autourl">
http://www.trnsys.com<br><br>
</a>"Providing software solutions for today's energy engineering
projects" <br>
****************************************************************************************<br>
</body>
</html>