Uwe,<br>
It may have something to do with the Type56 humidity model - walls
in Type56 are able to absorb and desorb moisture from the air.<br>
Kind regards,<br>
David<br><br>
<br>
At 11:40 3/9/2006, Uwe Meinhold wrote:<br>
<blockquote type=cite class=cite cite=""><font face="arial" size=2>Dear
TRNSYS User<br>
</font> <br>
<font face="arial" size=2>I checked a simple steady state problem in
trnsys15.<br>
I have a room: 50 m^3 with an air change rate of 0.7 per hour and a
source of 0.3 kg/h water. The outside and inside temperature is 20 °C and
the outside relative humidity is 0 (or 0.000000001%). <br>
</font> <br>
<font face="arial" size=2>The result of TRNSYS type 56 is 49.0263 %<br>
</font> <br>
<font face="arial" size=2>but the result of my calculation is 49.572%
(see enclosed pdf file).<br>
</font> <br>
<br>
<font face="arial" size=2>The differences comes with the source inside
the room. That means I go confirm with the psych - routine. <br>
</font> <br>
<font face="arial" size=2>Now my question is what makes the
difference?<br>
</font> <br>
<font face="arial" size=2>Thanks in advance<br>
</font> <br>
<br>
<br>
<br>
<br><br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@engr.wisc.edu<br>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" eudora="autourl">
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></blockquote>
<x-sigsep><p></x-sigsep>
****************************************************************************************<br>
Thermal Energy System Specialists (TESS), LLC <br>
David
BRADLEY
2916 Marketplace Drive - Suite 104 <br>
Partner
Madison, WI 53719 <br>
Phone: (608) 274-2577 USA <br>
Fax: (608) 278-1475 <br>
E-mail: bradley@tess-inc.com <br>
Web Pages:
<a href="http://www.tess-inc.com/" eudora="autourl">
http://www.tess-inc.com</a>
and
<a href="http://www.trnsys.com/" eudora="autourl">
http://www.trnsys.com<br><br>
</a>"Providing software solutions for today's energy engineering
projects" <br>
****************************************************************************************<br>
</body>
</html>