Hi,<br><br>
Are you referring to a “bouteille casse pression” <br>
(a bottle to break the pressure) when you mention
<font face="arial" size=2><b>equilibrium bottle </b></font>? <br><br>
A “bouteille casse pression” is usually inserted between<br>
a primary and a secondary pumping system to hydraulically <br>
decouple both systems. <br>
The most common term used in english is "common pipe" <br>
(see for example ASHRAE handbook-2000, page12.12 fig. 23) <br>
It is not a "tank" but usually as the form of an oversized
pipe<br>
with several inlet/outlets. You may want to model <br>
the “bouteille casse pression” as a flow mixer similar to type11d <br>
or as a small type4 tank. <br><br>
Voila !<br><br>
Michel Bernier<br><br>
P.S A similar question was asked on this forum on : Tue, 13 Jan 2004
13:12:27 <br>
***************************************<br>
Michel Bernier ing., Ph.D.<br>
Professeur<br>
Departement de genie mecanique<br>
Ecole Polytechnique de Montreal<br>
Case Postale 6079, Succ. "Centre-Ville"<br>
Montreal, Quebec Canada<br>
H3C 3A7<br>
Tél: (514) 340-4711 ext: 4381<br>
Fax: (514) 340-5917<br>
e-mail:michel.bernier@polymtl.ca<br>
***************************************<br><br>
<br><br>
<br>
At 09:13 2006-03-06, David Bradley wrote:<br>
<blockquote type=cite class=cite cite="">Hello Amandine,<br><br>
<blockquote type=cite class=cite cite=""><font face="arial" size=2><b>Is
the Type4 (storage tank) adapted to model an equilibrium
bottle?</b></font></blockquote><br>
I am not 100% certain what you mean by an equilibrium bottle. However,
Type4 is able to model any sized vertically cylindrical liquid filled
vessel provided that the volume of liquid inside the vessel does not
change. Type4 assumes that the vessel is always completely full. If you
need a variable volume tank, you can consider the use of Type39.<br><br>
<blockquote type=cite class=cite cite=""><font face="arial" size=2>I did
not manage to understand how Type4 is operating without any heating
element or heat exchanger;</font></blockquote><br>
The questions that you must answer in the TRNSYS Studio proforma can be a
little confusing. The easiest way to model a tank with no heating element
is to simply set the two "heating element power" parameters
each to zero. In that way, no matter what happens in terms of the tank's
controls, the elements are unable to provide any energy to the liquid. I
would not suggest answering the question "how many heating elements
to be modeled in this tank?" with 0 - simply leave the default
answer as "2." <br><br>
The way that the Type4 parameters are set up by default when you drag out
a new proforma into your simulation is without any heat exchangers so I
don't think that you need to do anything about those.<br><br>
Kind regards,<br>
David<br><br>
****************************************************************************************<br>
Thermal Energy System Specialists (TESS), LLC <br>
David
BRADLEY
2916 Marketplace Drive - Suite 104 <br>
Partner
Madison, WI 53719 <br>
Phone: (608) 274-2577 USA <br>
Fax: (608) 278-1475 <br>
E-mail: bradley@tess-inc.com <br>
Web Pages:
<a href="http://www.tess-inc.com /" eudora="autourl">
http://www.tess-inc.com </a>
and
<a href="http://www.trnsys.com/" eudora="autourl">
http://www.trnsys.com</a><br><br>
"Providing software solutions for today's energy engineering
projects" <br>
****************************************************************************************<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@engr.wisc.edu<br>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" eudora="autourl">
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></blockquote>
<x-sigsep><p></x-sigsep>
<br>
</body>
</html>