<html>
<body>
Dear Jörn,<br>
You are correct in your understanding that the Type56 internal
heating and cooling mechanisms are ideal and that there should be no
demand when the zone temperature is between the heating and cooling set
point, regardless of the time step. If you are seeing such behavior, you
should address the problem to your distributor.<br>
Kind regards,<br>
David <br><br>
At 01:22 AM 5/27/2005, Jörn von Grabe wrote:<br>
<blockquote type=cite class=cite cite=""><font face="arial" size=2>dear
all,<br>
<br>
the following situation occurred during a fairly simple simulation with
only one room, an irregular ventilation rate and an ambient temperature:
even though the room temperature was above the set temperature for the
heating the heating was turned on (sensible energy demand negative). at
first sight i thought this would happen because trnsys wants to avoid the
room temperature to drop below the set temperature during the time step.
but first of all it happens no matter how small my time steps are and
secondly it also happens even though the temperature increases due to the
heating (say 20° is my set temperature, 20,5° is my room temperature at
time step i and due to further heating it increases to 21° at time step
i+1). my question therefore is: can anyone explain to me the
trnsys-internal controlling mechanisms for heating? isn't it supposed to
be an ideal controller?<br>
<br>
thanks in advance,<br>
jörn<br>
<br>
</font>_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@engr.wisc.edu<br>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" eudora="autourl">
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></blockquote>
<x-sigsep><p></x-sigsep>
****************************************************************************************<br>
Thermal Energy System Specialists (TESS), LLC <br>
David
BRADLEY
2916 Marketplace Drive - Suite 104 <br>
Partner
Madison, WI 53719 <br>
Phone: (608) 274-2577 USA <br>
Fax: (608) 278-1475 <br>
E-mail: bradley@tess-inc.com <br>
Web Pages:
<a href="http://www.tess-inc.com/" eudora="autourl">
http://www.tess-inc.com</a>
and
<a href="http://www.trnsys.com/" eudora="autourl">
http://www.trnsys.com<br><br>
</a>"Providing software solutions for today's energy engineering
projects" <br>
****************************************************************************************<br>
</body>
</html>