<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005>Dear 
Hilde,</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005>the 
entries that you make in TRNBUILD for an internal shading are the following 
where the bol<SPAN class=625405310-13012005>d parameters are the keywords 
used in the bui file:</SPAN></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005><SPAN 
class=625405310-13012005></SPAN></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005><STRONG>reflishade</STRONG>=the reflection towards a 
window of the internal shading device - this is the material 
property - the reflectivity of the opaque material</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005><STRONG>refloshade</STRONG>=the reflection 
towards  the zone (backside of the shading)  - this is the material 
property - the reflectivity of the opaque material</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005><STRONG>Ishade</STRONG>=(1-Transmission)= opaque part 
of the window. <SPAN class=625405310-13012005>Please not that your data set 
includes transmission for one special position of the 
device.</SPAN></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005><SPAN 
class=625405310-13012005><STRONG>Ishade </STRONG>is</SPAN> an 
input because the transmission changes depending on the position of 
the shading device (closed/open)<STRONG>.</STRONG></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005><STRONG>CCISHADE</STRONG>=The part of the absorbed 
radiation on the internal shading that is transferred directly to the air node 
of the zone by convection.</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005><STRONG>RISHADE</STRONG>= additional heat resistance of 
the internal shading device.</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005>You 
will find an example for the calculation on page 49  of 
06-MultizoneBuilding.pdf in TRNSYS16.</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005>TRNSYS 
only needs the reflection of the opaque part = <SPAN 
class=625405310-13012005><STRONG>reflishade = (Reflection Coefficient of the 
shading device)/(1-Transmission data) </STRONG></SPAN></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005><SPAN 
class=625405310-13012005></SPAN>(this is e. g the reflectivity of the 
colour white or grey),</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005>The 
advantage is that the reflectivity of the opaque part doesn't change when 
you open or close the shading.</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005>Iref,z 
and I?</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005>We 
will add that to the manual:</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005><SPAN 
class=625405310-13012005>Iref,z ..... is the radiation coming from the zone due 
to reflection on walls or different windows hitting the backside <STRONG>(<SPAN 
class=625405310-13012005>refloshade)</SPAN></STRONG> of the internal 
shading</SPAN></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005><SPAN 
class=625405310-13012005>I ..... is the external radiation after the external 
shading hitting window and then the front side <STRONG>(</STRONG><SPAN 
class=625405310-13012005><STRONG>reflishade) </STRONG>of the internal 
shading<STRONG>.</STRONG></SPAN></SPAN></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005><STRONG>internal shading 
factor.</STRONG></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005>Due to 
the <SPAN class=625405310-13012005>internal shading factor</SPAN> is 
depending on the glazing, the resistances between the panes and towards the zone 
which are it self</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005>temperature depending, it can not be an input. 
</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005>Since 
TRNSYS16 the internal shading factor is an  output of  Balance 3 - solar 
balance for a window . </SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005>This 
balance was not possible with TRNSYS15 because you have to look only at the 
solar radiation coming through the window </SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005>in 
front of the internal shading. So for this balance in TRNSYS16 all radiation 
from other windows or reflected by the zone (<SPAN 
class=625405310-13012005><SPAN class=625405310-13012005>Iref,z) is 
excluded.</SPAN></SPAN></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005></SPAN></FONT><FONT face=Arial color=#0000ff 
size=2><SPAN class=625405310-13012005></SPAN></FONT><FONT face=Arial 
color=#0000ff size=2><SPAN class=625405310-13012005></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=625405310-13012005>best 
regards</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005>Torsten Welfoner</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=625405310-13012005></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT> </DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV></DIV>
  <DIV class=OutlookMessageHeader lang=de dir=ltr align=left><FONT face=Tahoma 
  size=2>-----Ursprüngliche Nachricht-----<BR><B>Von:</B> 
  trnsys-users-bounces@engr.wisc.edu [mailto:trnsys-users-bounces@engr.wisc.edu] 
  <B>Im Auftrag von </B>Hilde Breesch<BR><B>Gesendet:</B> Dienstag, 11. Januar 
  2005 13:34<BR><B>An:</B> TRNSYS users<BR><B>Betreff:</B> [TRNSYS-users] 
  internal shading Type56<BR><BR></FONT></DIV>
  <DIV><FONT face=Arial size=2>Dear Trnsys users,</FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>I have some problems to implement in Trnsys Type 
  56 with Prebid/Trnbuild an internal shading device with known data of 
  transmission, reflection and absorption coefficients. I also have calculated 
  the g-value of the whole system (glass + shading). I don't understand how 
  these data correspond to the input data in Prebid/Trnbuild:</FONT></DIV>
  <DIV><FONT face=Arial size=2>- internal shading factor: I have estimated this 
  by 1 - (g glass + sunblinds)/(g glass)</FONT></DIV>
  <DIV><FONT face=Arial size=2>- reflection coefficient of internal device: is 
  this the real reflection coefficient of the sunblinds of corresponds this to 
  REFLISHADE (as explained in the manual of Prebid/Trnbuild)</FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>I also don't understand the equation 4.8.8.1.44 
  in the Trnsys15 manual or (44) in Trnsys16 - Trnbuild manual that explains the 
  irradiation that is transmitted trough a window with an internal shading. Some 
  parameters in this equation aren't explained. Where e.g. can you give a value 
  to the 'solar transmittance of all window panes'? What is the difference 
  between Iref,z and I?</FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>best regards,</FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>Hilde Breesch<BR>PhD student Buildings & 
  Climatic Control<BR>Department of Architecture & Urban Planning<BR>Ghent 
  University<BR>J. Plateaustraat 22, B-9000 GENT<BR>tel. +32 9 264 78 61  
  fax. +32 9 264 41 85<BR>e-mail: <A 
  href="mailto:Hilde.Breesch@UGent.be">Hilde.Breesch@UGent.be</A><BR><A 
  href="http://allserv.ugent.be/~hbreesch/research">http://allserv.ugent.be/~hbreesch/research</A><BR></FONT></DIV></BLOCKQUOTE></BODY></HTML>