Ali,
The problem with just changing the fluid specific heat is that the
model still won't take into account the impact of the latent heat of
vaporization that occurs in air as it passes through the collector. If
you're going to approximate an air-based collector using Type50 you at
least need to put a psychrometrics component (Type33) after the
collector and pass it the collector outlet temperature and the
collector's /inlet /humidity ratio since the absolute humidity won't
change across the collector as the working fluid heats up. The Type33
will correct the exiting air state when the collector is heating the
working fluid. Correcting the air after calculating the collector
performance isn't ideal. You also have to be concerned about flow
through the collector when there isn't enough solar energy to heat up
the working fluid. If the fluid is cooling down instead of heating up
(and it certainly can unless your controls specifically prevent it) and
it cools down enough that it drops below the dewpoint temperature then
water is going to condense out of the air as it passes through. Again
the Type33 will correct the outlet air state and account for the
condensation energy but again, it will only correct it after the fact
and the correction won't impact the collector's performance.
A preferable solution would be that if you have access to it there are
a number of air-based PV/T models available in the TESS Electrical library
kind regards,
David
On 05/25/2021 09:05, Ali Shahrouzian via TRNSYS-users wrote:
>
> Hi,
>
> I’m modelling an air-based PVT system for heating application. Do you
> think I could use the type 50 as an air-based PVT collector if I
> specify the fluid thermal capacitance of 1 (kJ/kg.K) instead of 4.19?
>
> Thanks in advance
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210525/f5b7f762/attachment.html>
More information about the TRNSYS-users
mailing list