The controller can make one control decision per time step. When the
controller decides to turn on the cooling equipment then the cooling
equipment has to stay on for 5 minutes, driving the temperature of the
space downwards, perhaps beyond the limit of the dead band. If you use a
1 minute timestep instead then the controller has a chance every minute
to turn the cooling equipment back off, limiting the temperature
overshoot in the building.
kind regards,
David
On 05/25/2021 08:01, asmin aryal wrote:
> Dear Sir,
> I am cooling type 56 building with type type 752 (Simple Cooling Coil
> Using Bypass Fraction Approach; Temperature Controlled) by introducing
> the cool air via ventilation to type 56.
> I am controlling the room air temperature by type 2: aquastatC
> controller. When i run the simulation with 5 min time step, the
> controller cannot control the room air temperature within the dead
> band but when i run the simulation with 1 min time step it can control
> the room temperature within the dead band.
> What may be the possible reason.
> Looking forward to your answer.
> image.png
>
> image.png
> Sincerely
> Ashmin Aryal
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210525/b6faea43/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 320282 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210525/b6faea43/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 816505 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210525/b6faea43/attachment-0003.png>
More information about the TRNSYS-users
mailing list