[TRNSYS-users] Floor heating in a freezer
David BRADLEY
d.bradley at tess-inc.com
Fri Mar 26 21:29:04 PST 2021
I suspect that you're going to have some trouble with the EMPA model. It
has some restrictions on the ratio of the center to center pipe distance
to the floor thickness. Also, that thickness of concrete might give
TRNBuild a hard time in determining the transfer function coefficients.
I realize you said you do not have Type1267 but it would allow you to
define such an arrangement. You'd define a thin top layer for the floor
in 56 as a BOUNDARY and then you'd define the concrete that makes up the
rest of the floor as a material in Type1267. You can then tell it how
the pipes run through the concrete.
best,
David
On 03/26/2021 16:01, leen peeters via TRNSYS-users wrote:
> Hi all,
>
> I need to model a freezer (-16 to -22 degrees Celcius), with floor
> heating at pipe-to-pipe distances of 60 cm. Floor is composed of
> (bottom to top) 25 cm concrete with the floor heating, 20 cm of
> insulation on top of that and 10 cm of concrete on top of the insulation.
> Is the EMPA model embedded in type 56 suited for this?
>
> Another case is simply the floor heating concrete layer, and no layers
> on top. Some question here but with distances between pipes equaling
> 50 cm.
>
> Thanks
> Leen
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210326/f2a92997/attachment.html>
More information about the TRNSYS-users
mailing list