[TRNSYS-users] inconsistency in flow rate units
David BRADLEY
d.bradley at tess-inc.com
Mon Jun 28 07:14:44 PDT 2021
Changing the units of an input in a proforma does not create an
automatic conversion. The model requires that the flow rate inputs be
given in kg/h. If your upstream component is outputting a flowrate it
kg/s then you will need to put an equation in between it and the Type534
in order to manually convert the value.
kind regards,
David
On 06/26/2021 01:47, Maryam Khademi via TRNSYS-users wrote:
>
> Hi guys,
>
> How I can define variable flow rate for storage tank ports of type 534?
>
> And I defined flow rates of tanks in kg per second but surprisingly
> when I plot these flow rates, are multiplied by 1000.
>
> I cannot find what is the reason!!!
>
> Sent from Mail <https://go.microsoft.com/fwlink/?LinkId=550986> for
> Windows 10
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210628/95e0a12d/attachment.html>
More information about the TRNSYS-users
mailing list