[TRNSYS-users] Power use of heat pump is constant
David BRADLEY
d.bradley at tess-inc.com
Mon Jan 4 06:38:38 PST 2021
Amirreza,
If the air and water conditions at the inlet of your heat pump are
always outside the range of the performance map then the power and COP
will always come back with the same values. Of course it is also
possible that the performance map that you are using is set up in such a
way that the COP is always the same no matter what the inlet conditions.
The *.lst file may have some additional clues in it.
kind regards,
David
On 01/03/2021 05:16, Heidari Amirreza via TRNSYS-users wrote:
>
> Hello,
>
>
> To model a heat pump water heating system I am using type 938. In
> theory, the COP of the heat pump should decrease with the increase of
> storage tank temperature. Also, it should increase with the increase
> of outdoor air temperature. However, using type 938 the power
> consumption is always the same. Would you please let me know how it
> can be modified in my simulation?
>
>
> ---------------------------------------
>
> /*Doctoral Assistant, E**cole Polytechnique Fédérale de Lausanne
> (EPFL), Switzerland*
> /
>
> /*
> */
>
> /*Email:*/
>
> /amirreza.heidari at epfl.ch/
>
> /amirrezaheidarysbu at gmail.com/
>
> /
> /
>
> /*Phone: *+41 21 69 57221/
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210104/ea959ac1/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: pastedImage.png
Type: image/png
Size: 32573 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210104/ea959ac1/attachment-0001.png>
More information about the TRNSYS-users
mailing list