[TRNSYS-users] Problem matching surfaces Trnsys3d
David BRADLEY
d.bradley at tess-inc.com
Mon Jan 4 06:33:52 PST 2021
Toni,
If you haven't already done so, you need to activate the first floor
and draw lines on its roof/ceiling that correspond to the footprint of
the second floor. The same holds true for walls and floors,
SketchUp/Trnsys3D is looking at the vertices of all your surfaces and if
two surfaces have precisely the same vertices then they will be
recognized as matching.
kind regards,
David
On 01/04/2021 08:24, Toni Calabrese via TRNSYS-users wrote:
>
> Hi,
>
> I have a problem with the "match surfaces" function in SketchUp. I
> have a building in which the second floor is smaller compared to the
> first floor (see the image). When I "match the surfaces", it tells me
> that the floor of the second floor is an external roof and seems that
> it does not recognize that the floor of the second floor is connected
> with the ceiling of the first floor. If the two floors have the same
> surfaces, it works perfectly but in this special case it does not
> work. Someone can help me?
>
> Thanks a lot for any help.
>
> ------------------------------------------------------------------------
>
> *Toni Calabrese*, MSc.
>
> Wissenschaftlicher Projektmitarbeiter
>
> toni.calabrese at spf.ch <mailto:toni.calabrese at spf.ch>
> |toni.calabrese at ost.ch <mailto:toni.calabrese at ost.ch>
>
> T +41 58 257 4827
>
> SPF Institut für Solartechnik
>
> OST – Ostschweizer Fachhochschule
>
> Oberseestr. 10 | CH-8640 Rapperswil | Switzerland | _www.spf.ch
> <http://www.spf.ch>_| _www.ost.ch <http://www.ost.ch>_
>
> OST – Ostschweizer Fachhochschule ist der Zusammenschluss aus FHS
> St.Gallen, HSR Rapperswil und NTB Buchs.
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210104/e7696dad/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 87747 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210104/e7696dad/attachment-0001.png>
More information about the TRNSYS-users
mailing list