[TRNSYS-users] VirtualSurface
David BRADLEY
d.bradley at tess-inc.com
Fri Apr 30 09:22:40 PDT 2021
Karol,
I think your picture is correct.
The process for setting it up can be a little confusing. My
understanding of how to set up the second case is to draw both Zone1 and
Zone2 separated by a VirtualSurface in Trnsys3d. I assume there is some
way of doing the same in TRNLizard but I'm afraid I'm not familiar with
that tool. Once you import the *.idf file into TRNBuild, the virtual
surface will disappear. You then add Zone2 to Zone1 so that they become
two airnodes of a single zone. To do this, you open the zone/airnode
that you're going to move and you click on the button in the upper left
corner that looks like a u-shaped arrow.
Since the virtual surface that separates the two airnode has
disappeared you no longer have an adjacent surface through which to
define the air flow coupling. Instead, you click on the "coupling"
button in the airnode window (upper right) and define the coupling there.
best,
David
On 04/30/2021 08:01, Karol BANDURSKI via TRNSYS-users wrote:
>
> Dear Expert,
>
> I have tackled this topic a few times but I am still not sure if I
> understand the idea of Virtual Surface.
>
> Could you write me if enclosed sketch properly describe heat exchange
> in the zone in the context of Virtual surface?
>
> Kind regards,
>
> Karol
>
> --------------------------------------------------------------------
>
> Karol BANDURSKI Ph.D.
>
> Faculty of Environmental and Energy Engineering
>
> Division of Heating, Air Conditioning and Air Protection
>
> Poznan University of Technology
>
> www.put.poznan.pl/~karol. bandurski
> <http://www.put.poznan.pl/~karol.bandurski>
>
> https://www.researchgate.net/profile/Karol_Bandurski
> <https://www.researchgate.net/profile/Karol_Bandurski>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210430/15281502/attachment.html>
More information about the TRNSYS-users
mailing list