[TRNSYS-users] Using radiation processor (type 99, type 16i or any ) with 1 min measured global and diffused radiation on horizontal surface
David BRADLEY
d.bradley at tess-inc.com
Thu Oct 8 06:22:43 PDT 2020
Ashmin,
It may be possible to use Type99 in the manner that you want but I
would recommend that you use Type9 to read the minute data and then
Type16 to process it and compute the values on the other surfaces.
kind regards,
David
On 10/07/2020 23:32, asmin aryal wrote:
> Dear all,
> I was using type 99 for reading the data and was using it as a
> radiation processor (with hourly input data for global radiation on
> horizontal and diffuse radiation on horizontal). But now I need to
> validate my simulation with my experimental work . *I have /weather
> data from measurements (global radiation on horizontal and diffuse
> radiation on horizontal) /at/1 min interval for some particular days.
> /* I couldn’t obtain tilted surface radiation (radiation on the
> building facade) within 1 min. data. My question is how to input 1 min
> global and diffuse horizontal radiation data and get the value for
> each facade of the building using the radiation processor (be it type
> 99 or type 16 i or any other radiation processor).
> I tried to input the weather data similar to what we do for hourly
> data by changing the hours in minutes as follows but i couldn't get
> any data for radiation in other tilted surfaces (building walls).
> <userdefined> <longitude> -100.49 ! east of greenwich: negative
> <latitude> 13.75 ! Bangkok Thailand <gmt> 7 ! time shift from GMT
> east: positive (minutes) - if solar time-> write solar <interval> 1 !
> Data file time interval between consecutive lines <firsttime> 0 ! Time
> corresponding to first data line (minutes) <var> IBEAM_H <col> 0
> <interp> 0 <add> 0 <mult> 1 <samp> -1 !...to get radiation in W/m?
> <var> IBEAM_N <col> 0 <interp> 0 <add> 0 <mult> 1 <samp> 0 !...to get
> radiation in W/m? <var> IDIFF_H <col> 5 <interp> 0 <add> 0 <mult> 1
> <samp> -1 !...to get radiation in W/m? <var> IGLOB_H <col> 4 <interp>
> 0 <add> 0 <mult> 1 <samp> -1 !...to get radiation in W/m? <var> TAMB
> <col> 6 <interp> 2 <add> 0 <mult> 1 <samp> 0 !...to get ?C <var> RHUM
> <col> 7 <interp> 1 <add> 0 <mult> 1 <samp> 0 !...to get relative
> humidity in % <var> WSPEED <col> 0 <interp> 1 <add> 0 <mult> 1 <samp>
> 0 !...to get wind speed in m/s <var> WDIR <col> 0 <interp> 1 <add> 0
> <mult> 1 <samp> 0 !...to get wind direction in degree <var> T_sky
> <col> 8 <interp> 2 <add> 0 <mult> 1 <samp> 0 !...to get ... in ...
> <var> W_amb <col> 9 <interp> 0 <add> 0 <mult> 1 <samp> 0 !...to get
> ... in ... <var> GRD <col> 10 <interp> 0 <add> 0 <mult> 1 <samp> 0
> !...to get ... in ... <var> udef4 <col> 0 <interp> 0 <add> 0 <mult> 1
> <samp> 0 !...to get ... in ... <data> 1 1 0 1.485 -0.209 25.479 96.329
> 17.39802308 0.0199 0.2 1 1 1 1.955 0.032 25.723 96.315 17.75626828
> 0.0202 0.2 1 1 2 1.779 0.212 25.616 96.394 17.60553878 0.0201 0.2 1 1
> 3 1.897 -0.329 25.582 96.284 17.54582309 0.0200 0.2 1 1 4 1.897 0.032
> 25.594 96.335 17.56796545 0.0200 0.2
> I am unaware of how to input minutes data in type 99 and get the
> values of radiation on tilted surfaces (building walls) . Please let
> me know how to do it. I will be indebted.
> Thanking you
> Ashmin Aryal
> King Mongkut's University of Technology Thonburi (KMUTT), Thailand
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20201008/dc76a638/attachment-0001.html>
More information about the TRNSYS-users
mailing list