[TRNSYS-users] Type 941(Air to water heat pump)
Hüseyin Günhan Özcan
huseyin.ozcan at yasar.edu.tr
Fri Mar 27 09:15:26 PDT 2020
Dear Jeff,
I applied the same working procedure while modeling the system. In my case I am using a split type air conditioner and it has no fresh air option (no ventilation). It only circulates and conditions the indoor air.
Therefore, I connected the weather data both the building and heat pump. The inlet temperature of the building change by this connection. Then, I connected the inside air temperature change to the heat pump return air under using thermostat. I also switched off the heating, cooling and ventilation options in Type 56.
I thought it was a logical approach by providing “All need to be answered every time” case.
But now I faced to apply reverse process. I will try to do this new proposed way.
Thanks in advance.
HG Ozcan
From: Jeff Thornton <thornton at tess-inc.com>
Sent: Friday, March 27, 2020 3:59 PM
To: Hüseyin Günhan Özcan <huseyin.ozcan at yasar.edu.tr>
Cc: TRNSYS users mailing list at OneBuilding.org <trnsys-users at lists.onebuilding.org>; David BRADLEY <d.bradley at tess-inc.com>; Muhammad Zeeshan <zeeshanmuhammad922 at gmail.com>
Subject: Re: [TRNSYS-users] Type 941(Air to water heat pump)
Huseyin,
You’ll need to add a ventilation stream to the building and then set the ventilation inputs (temperature, humidity, flow rate) as inputs. There are example projects and documentation on how to do that.
On a broader scale, remember that each component, piece of equipment etc needs to be fully connected in TRNSYS like a real piece of equipment. The trnsys connections are equivalent to pipes and wires in a real system. Where is the air coming from, where is it going, what’s going to turn my device on and off, etc. All need to be answered every time.
Jeff
Sent from my iPhone
On Mar 27, 2020, at 10:46 AM, Hüseyin Günhan Özcan <huseyin.ozcan at yasar.edu.tr<mailto:huseyin.ozcan at yasar.edu.tr>> wrote:
Dear Jeff,
No. I have just connected the room air temperature and reletive humudity outputs of Type 56 to the return air temperature and return air relative humudity inputs of Type 922c inputs.
There is no opportunity for inverse relation from heat pump to building.
I checked under enabling and disenabling ventilation, heating and cooling options in TRNBuild.
Regards.
Huseyin
From: Jeff Thornton <thornton at tess-inc.com<mailto:thornton at tess-inc.com>>
Sent: Friday, March 27, 2020 3:34 PM
To: TRNSYS users mailing list at OneBuilding.org <trnsys-users at lists.onebuilding.org<mailto:trnsys-users at lists.onebuilding.org>>
Cc: Hüseyin Günhan Özcan <huseyin.ozcan at yasar.edu.tr<mailto:huseyin.ozcan at yasar.edu.tr>>; David BRADLEY <d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>>; Muhammad Zeeshan <zeeshanmuhammad922 at gmail.com<mailto:zeeshanmuhammad922 at gmail.com>>
Subject: Re: [TRNSYS-users] Type 941(Air to water heat pump)
Simple question; did you connect the outputs of the heat pump ( temperature, humidity and flow rate) back to the building as ventilation inputs?
Jeff
Sent from my iPhone
On Mar 27, 2020, at 10:31 AM, David BRADLEY via TRNSYS-users <trnsys-users at lists.onebuilding.org<mailto:trnsys-users at lists.onebuilding.org>> wrote:
Hüseyin,
I am not clear on what you mean by "it" doesn't change. I would recommend that you send the project, weather file, and heat pump files to your distributor so that they can have a look. If you aren't sure who to contact, please email me.
David
On 03/27/2020 10:27, Hüseyin Günhan Özcan wrote:
Dear David,
Thanks for your rapid reply. As you said, I turned off the automatic heating and cooling. I can see the temperature of the zone is floating. I also used a second stage thermostat (type 1503) and adjust the high and low stage temperatures.
However, it does not change although the temperature floats between 19 °C and 30 C°.
Regards.
HG Ozcan
From: David BRADLEY <d.bradley at tess-inc.com><mailto:d.bradley at tess-inc.com>
Sent: Friday, March 27, 2020 3:12 PM
To: Hüseyin Günhan Özcan <huseyin.ozcan at yasar.edu.tr><mailto:huseyin.ozcan at yasar.edu.tr>; TRNSYS users mailing list at OneBuilding.org <trnsys-users at lists.onebuilding.org><mailto:trnsys-users at lists.onebuilding.org>
Cc: Muhammad Zeeshan <zeeshanmuhammad922 at gmail.com><mailto:zeeshanmuhammad922 at gmail.com>
Subject: Re: [TRNSYS-users] Type 941(Air to water heat pump)
Hüseyin
This may seem very basic but make sure that you have turned off the automatic heating and cooling in TRNBuild so that the temperature of your zone is floating. You can verify this by running your simulation; the zone temperature should more or less follow the ambient temperature. You will then implement a thermostat to watch the zone temperature and turn on/off the heat pump accordingly.
If that is what you are doing already and the power and capacity of the heat pump is not changing at all then it must mean that neither the return air temperature nor the water inlet temperature is changing at all. It could also mean that the return air temperature and inlet water temperature are outside the range of data values given in the data file. The routine that reads the data file and interpolate within the range but cannot extrapolate beyond the range given.
kind regards,
David
On 03/27/2020 09:29, Hüseyin Günhan Özcan wrote:
Dear all,
I have a similar question about modeling air source heat pump.
In my case I am working the model inverter heat pump so I selected the multi stage heat pump (Type 922c).
Meanwhile, I connected its return temperature value to the Type 56 indoor temperature (I am following a single room) and I also use Type 15-6 for outdoor conditions. Although I make some changes in the building file (internal heat gain, regimes, etc.) and weather data the model shows always the same values.
Therefore, I realized that it only works based on external catalogue values. But, it does not make sense. Do you have an idea about this case ? How can type 922c operates based on temperature variations belongs to the building.
Another question is how can I change the catalogue values ? (I have no problem in proforma including parameter, input and output parts).
Thanks in advance.
Huseyin Gunhan Ozcan
Visiting Researcher
Porto Uni., Dept. of Mech. Eng.
<image001.png>
From: TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org><mailto:trnsys-users-bounces at lists.onebuilding.org> On Behalf Of David BRADLEY via TRNSYS-users
Sent: Friday, March 27, 2020 1:45 PM
To: TRNSYS users mailing list at OneBuilding.org <trnsys-users at lists.onebuilding.org><mailto:trnsys-users at lists.onebuilding.org>
Cc: David BRADLEY <d.bradley at tess-inc.com><mailto:d.bradley at tess-inc.com>; Muhammad Zeeshan <zeeshanmuhammad922 at gmail.com><mailto:zeeshanmuhammad922 at gmail.com>
Subject: Re: [TRNSYS-users] Type 941(Air to water heat pump)
Muhammad,
Please refer to the Type941 documentation. It explains how the external files and the parameters relate to each other to compute the overall capacity and power consumption of the heat pump.
The evaporator does not really need to be designed more than to choose a machine with an appropriate rated capacity. Traditionally that might mean adding a safety factor to the peak cooling load (10% is often used) and then selecting a machine that will meet that capacity. Also bear in mind that Type941 models a single speed (ie single capacity) heat pump that is either on or off. Depending on how variable the load in your building it, you might want to meet that load with multiple smaller heat pumps rather than one big one.
kind regards,
David
On 03/27/2020 08:02, Muhammad Zeeshan via TRNSYS-users wrote:
Hello Everyone,
I am working on cooling a building with type 41(air to water source heat pump). The cooling load of the building is 25 tons. I want to know
1)- how the compressor power will be calculated? as the external files of type 941 contains fractions of compressor power which shows no link to the equations provided in manual. How to link the external file with the provided equations?
2)-As the cooling load of the building is 25 tons, how to design the evaporator for this building load?
Your help in this regard will be highly appreciated.
Regards,
Muhammad Zeeshan
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org<mailto:TRNSYS-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com
http://www.trnsys.com
Bu elektronik postada bulunan tum fikir ve gorusler ve ekindeki dosyalar sadece adres sahip/sahiplerine ait olup,
Yasar Universitesi bu mesajin icerigi ile ilgili olarak hic bir hukuksal sorumlulugu kabul etmez. Eger gonderilmesi
dusunulen kisi veya kurulus degilseniz, lutfen gonderen kisiyi derhal haberdar ediniz ve mesaji sisteminizden siliniz.
The information contained in this e-mail and any files transmitted with it are intended solely for the use of the
individual or entity to whom they are addressed Yasar University does not accept legal responsibility for the
contents. If you are not the intended recipient, please immediately notify the sender and delete the message from your system.
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com
http://www.trnsys.com
Bu elektronik postada bulunan tum fikir ve gorusler ve ekindeki dosyalar sadece adres sahip/sahiplerine ait olup,
Yasar Universitesi bu mesajin icerigi ile ilgili olarak hic bir hukuksal sorumlulugu kabul etmez. Eger gonderilmesi
dusunulen kisi veya kurulus degilseniz, lutfen gonderen kisiyi derhal haberdar ediniz ve mesaji sisteminizden siliniz.
The information contained in this e-mail and any files transmitted with it are intended solely for the use of the
individual or entity to whom they are addressed Yasar University does not accept legal responsibility for the
contents. If you are not the intended recipient, please immediately notify the sender and delete the message from your system.
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com
http://www.trnsys.com
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org<mailto:TRNSYS-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
Bu elektronik postada bulunan tum fikir ve gorusler ve ekindeki dosyalar sadece adres sahip/sahiplerine ait olup,
Yasar Universitesi bu mesajin icerigi ile ilgili olarak hic bir hukuksal sorumlulugu kabul etmez. Eger gonderilmesi
dusunulen kisi veya kurulus degilseniz, lutfen gonderen kisiyi derhal haberdar ediniz ve mesaji sisteminizden siliniz.
The information contained in this e-mail and any files transmitted with it are intended solely for the use of the
individual or entity to whom they are addressed Yasar University does not accept legal responsibility for the
contents. If you are not the intended recipient, please immediately notify the sender and delete the message from your system.
Bu elektronik postada bulunan tum fikir ve gorusler ve ekindeki dosyalar sadece adres sahip/sahiplerine ait olup,
Yasar Universitesi bu mesajin icerigi ile ilgili olarak hic bir hukuksal sorumlulugu kabul etmez. Eger gonderilmesi
dusunulen kisi veya kurulus degilseniz, lutfen gonderen kisiyi derhal haberdar ediniz ve mesaji sisteminizden siliniz.<br><br>
The information contained in this e-mail and any files transmitted with it are intended solely for the use of the
individual or entity to whom they are addressed Yasar University does not accept legal responsibility for the
contents. If you are not the intended recipient, please immediately notify the sender and delete the message from your system.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20200327/57288c76/attachment-0001.html>
More information about the TRNSYS-users
mailing list