[TRNSYS-users] TRNSYS time equation
Marion Hiller
Hiller at Transsolar.com
Thu Mar 26 01:53:05 PDT 2020
Dear Adnan,
you may use Type 14 got the time depending set temperature as an output which you may use for further control.
Keep in mind that controls by equation may cause instability. It is recommended to use a controller Type with temperature bands (e.g. Type 2)
Marion
Marion Hiller
+49 711 679 76 32 | hiller at transsolar.com
Transsolar SoftwareEngineering
Stuttgart | Munich | Paris | New York
Transsolar Energietechnik GmbH | Curiestrasse 2 | 70563 Stuttgart | Germany
CEO: Matthias Schuler, Thomas Auer, Stefan Holst, Dieter Schnelle
Registered at Amtsgericht Stuttgart HRB 23347 | USt-IdNr.: DE 152272639
Von: TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org> Im Auftrag von adnan rasheed via TRNSYS-users
Gesendet: Donnerstag, 26. März 2020 09:31
An: TRNSYS users mailing list at OneBuilding.org <trnsys-users at lists.onebuilding.org>
Cc: adnan rasheed <adnan.upm.spain at gmail.com>
Betreff: Re: [TRNSYS-users] TRNSYS time equation
Dear Marion Hiller ,
i checked Type 14 output will not work in this situation.
Actually i want to control natural ventilation window open and close according to the set point, at the corresponding time span. As i write before temperature is room temperature, on behalf of that window should be open and close. if room temperature is high than the set value at particular time span window should open (natural ventilation).
00 to 5h.... temp set point 18 C
5-10h.... temperature set point 22 C
10-18h....23 C
18 -24h...24 C
Thanks
On Thu, Mar 26, 2020 at 4:58 PM Marion Hiller via TRNSYS-users <trnsys-users at lists.onebuilding.org<mailto:trnsys-users at lists.onebuilding.org>> wrote:
Hello Adnan,
I recommend to use Type 14 instead of an equation .
Marion
Marion Hiller
hiller at transsolar.com<mailto:hiller at transsolar.com>
Transsolar SoftwareEngineering
Stuttgart | Munich | Paris | New York
Transsolar Energietechnik GmbH | Curiestrasse 2 | 70563 Stuttgart | Germany
CEO: Matthias Schuler, Thomas Auer, Stefan Holst, Dieter Schnelle
Registered at Amtsgericht Stuttgart HRB 23347 | USt-IdNr.: DE 152272639
Von: TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org<mailto:trnsys-users-bounces at lists.onebuilding.org>> Im Auftrag von adnan rasheed via TRNSYS-users
Gesendet: Donnerstag, 26. März 2020 08:26
An: TRNSYS users mailing list at OneBuilding.org <trnsys-users at lists.onebuilding.org<mailto:trnsys-users at lists.onebuilding.org>>
Cc: adnan rasheed <adnan.upm.spain at gmail.com<mailto:adnan.upm.spain at gmail.com>>
Betreff: [TRNSYS-users] TRNSYS time equation
Hello everyone,
i want to use an equation for two control parameters time and temperature . like my control is
00 to 5h.... temp set point 18 C
5-10h.... temperature set point 22 C
10-18h....23 C
18 -24h...24 C
i need to get output as 0 or 1, i am already using the following equation which is only allowing me to set one temperature set point, i need to set different temperature set points during complete one day.
GT(Temp,20)
how i can add time function with this equation
Thanks
--
Adnan Rasheed
Post-doc Research Fellow
Kyungpook National University
Daegu, South Korea.
+82-102762-0105
adnan.upm.spain at gmail.com<mailto:adnan.upm.spain at gmail.com>, adnanrasheed at knu.ac.kr<mailto:adnanrasheed at knu.ac.kr>
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org<mailto:TRNSYS-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
Adnan Rasheed
Post-doc Research Fellow
Kyungpook National University
Daegu, South Korea.
+82-102762-0105
adnan.upm.spain at gmail.com<mailto:adnan.upm.spain at gmail.com>, adnanrasheed at knu.ac.kr<mailto:adnanrasheed at knu.ac.kr>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20200326/1d1ae4be/attachment-0001.html>
More information about the TRNSYS-users
mailing list