You can make the ground floor slab of your building into a BOUNDARY
wall and set its "back side" condition to a user-defined temperature.
You'll then get the option to define that temperature as a constant
value, a scheduled temperature, or an input. Choose the "constant value"
option and set it to 11C.
Do keep in mind that what you are setting is the temperature of the
interface between the back side of the boundary wall (the slab) and the
ground temperature. You are NOT setting a deep earth temperature. If
your 11C is a deep earth temperature then you might look at some of the
other options that TRNSYS offers for dealing with the energy transfer
between a building and the ground.
kind regards,
David
On 10/01/2019 09:45, Arne Hübner via TRNSYS-users wrote:
>
> Hello TRNSYS-User,
>
> how can I set a fixed Ground temperature of 11°C for the hole year in
> TRNBuild?
>
> Kind regards,
>
> Arne
>
> Gesendet von Mail <https://go.microsoft.com/fwlink/?LinkId=550986> für
> Windows 10
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191003/a9fee049/attachment.html>
More information about the TRNSYS-users
mailing list