[TRNSYS-users] how to fix power consumption of a pump
David BRADLEY
d.bradley at tess-inc.com
Mon May 13 07:24:40 PDT 2019
Sajid,
You'll need to look at the variable speed pump Type's parameters.
Most VSP models ask for the coefficients of the polynomial that relates
power consumption to flow rate. If you set that polynomial up with only
one coefficient whose value is 1 then your polynomial comes down to p =
pRated. If you set the number of coefficients to 4 and give the first
three a value of 0 and the last one a value of 1 then your polynomial is
p = pRated*(m/mRated)**3
kind regards,
David
On 05/11/2019 13:59, MEHMOOD Sajid via TRNSYS-users wrote:
> Dear Trnsys Users,
>
> I have a question regarding Pump Pump Consumption (Variable Speed
> Pump). I used forcing function to control mass flow rate of pump. And
> plotted result shows that mass flow rate is different in different
> hours of the day. But power consumption of pump is constant. Common
> sense says that when pump flow rate is different, power consumption by
> pump should be different. is not it?
> Please see attached figures (plotted results).
>
> Please give your opinion in this regard.
>
> Thank you.
>
> Best Regards,
> Sajid
> The University of Edinburgh is a charitable body, registered in
> Scotland, with registration number SC005336.
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190513/2424ef51/attachment.html>
More information about the TRNSYS-users
mailing list