If the solar radiation data that you have is the instantaneous
measurement, or the average rate over the 10-minute period, in W/m2 then
the conversion is:
10 W/m2 =>10 J/s.m2 * 3600 s/hr * 1 kJ/1000 J = 36 kJ/h.m2
If the data you have is the integrated total then the conversion is
different:
10 W.hr/m2 => 10 J.hr/s.m2 * 1 kJ/1000 J * 3600 s/hr = 36 kJ/m2
But the radiation processor requires the rate so we must divide by the
timestep of the integration period:
36 kJ/m2 / 10 minutes * 60 minutes/hr = 216 kJ/h.m2
Bottom line: make sure you know the units of the measurement which you
were given.
Jeff
---
Jeff Thornton
President - TESS LLC
3 N. Pinckney Street, Suite 202, Madison WI USA 53703
Office: (608) 274-2577 Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton at tess-inc.com
On 01/06/2019 7:47 pm, adnan rasheed via TRNSYS-users wrote:
> Hello everyone,
>
> i have a question about use of 10 min interval solar radiation data used for TYPE 9 (data reader) and TYPE 16 (radiation processor). i have 10 min interval solar radiation data in W/m2, i need to convert this data to KJ/m2/hr to used in TRNSYS. how should i do among followings...
>
> 10 W/m2 .......... 10 *1000/ 3600 = 10 * 3.6 KJ/m2/hr. or i need to convert it as
> 10 W/m2.......... 10 * 1000/600 = 10 * 0.6 KJ/m2/10min
>
> Thanks in advance..
>
> --
>
> Adnan Rasheed
> PhD Researcher
> Kyungpook National University
> Daegu, South Korea.
> +82-102762-0105
> adnan.upm.spain at gmail.com, adnanrasheed at knu.ac.kr
>
> [2]
> Sender notified by
> Mailtrack [2] 01/07/19, 10:39:34 AM
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org [1]
Links:
------
[1]
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
[2]
https://mailtrack.io?utm_source=gmail&utm_medium=signature&utm_campaign=signaturevirality5&
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190106/685f3e21/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: blocked.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190106/685f3e21/attachment.gif>
More information about the TRNSYS-users
mailing list