Tue Feb 26 03:04:59 PST 2019
Dear Camille,
Every energy balance has a boundary.
The boundary of the energy balance 4 is the inside surface of walls, floors, ceilings/roofs and windows.
The Energy balance 4 doesn't include the constructions themselves!!
In other words, B4_QTRANS is the energy that leaves/enters a thermal zone by conduction into/out of the construction of the side of walls, floors, ceilings/roofs and windows facing the zone.
Best regards,
Marion
-----------------------------------------------------------------------------------------------------------------------------------------------------------
Dipl.-Ing. Marion Hiller
TRANSSOLAR Energietechnik GmbH
Stuttgart - Munich - New York - Paris
t: +49.711.67976.0<tel:%2B49.711.67976.27> f: +49.711.67976.11<tel:%2B49.711.67976.11>
www.transsolar.com/<http://www.transsolar.com/>
KlimaEngineering - Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäuden
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347 / Steuernummer: 99073/00911 / USt-IdNr.: DE 152272639
Geschäftsführer: Matthias Schuler, Thomas Auer, Stefan Holst, Dieter Schnelle
Von: TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org> Im Auftrag von BERNARD Camille via TRNSYS-users
Gesendet: Donnerstag, 21. Februar 2019 09:05
An: trnsys-users at lists.onebuilding.org
Cc: BERNARD Camille <camille.bernard at etamine.coop>
Betreff: [TRNSYS-users] B4_QTRANS
Hello,
I model a typical office building : one intermediate level of a tower.
In order to understand the energy balance, I have looked at each variable of balance 4.
I have difficulties to understand QTRANS, and the explanation in the documentation is quite vague :
Balance 4 is a "balance for zones" : results are given by zone.
QTRANS is described as : "transmission into the surface from inner surface node (might be stored in the wall, going to a slab cooling or directly transmitted)" : it refers to surface and not to zone...
Do you know what does it represent and how it is calculated ?
Thank you,
Best regards,
Camille Bernard | Chargée d'études
[Das Bild wurde vom Absender entfernt. Etamine]
----------------------------------------------
www.etamine.coop<http://www.etamine.coop/>
83-85 boulevard Vincent Auriol - 75013 Paris
mobile : 07.63.45.95.01
camille.bernard at etamine.coop
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190226/b7c6763e/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 579 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190226/b7c6763e/attachment.jpg>
More information about the TRNSYS-users
mailing list