[TRNSYS-users] How to conduct parametric analysis in TRNSYS
David BRADLEY
d.bradley at tess-inc.com
Tue Dec 10 10:13:27 PST 2019
Salma,
There are (as usual) a number of different ways of having all the
results from a parametric run put into the same output file. One way is
to use a Type25 printer as an output device in your simulation and to
set it to "append" mode instead of "overwrite mode." The mode is
controlled by a parameter. The other thing you'll need to do is to make
sure that the name of the output file is NOT the same as the name of
your input file, otherwise there will be one output file produced per
table run. Note that a number of the standard printer output components
in TRNSYS allow the switch between append and overwrite mode.
kind regards,
David
On 12/08/2019 07:33, SALMA LAHMAR via TRNSYS-users wrote:
> I have to run a lot of simulations to calculate the building energy
> consumption depending on the value of different parameters.
> I tried to use trnedit to make a table but I don't know how to have a
> result of all simulation in one output file like
> : \Examples\Parametric Runs\SDHW-ParametricRuns in trnsys.
> thanks in advance
> ᐧ
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191210/6a728493/attachment.html>
More information about the TRNSYS-users
mailing list