Yeyson, 

The reason the outlet temperatures are different is that in the first
project you have a pump and a controller to modulate the flow through
the ground heat exchanger. In the second project you have no flow... 

The error you refer to is that Type 99 cannot read the external data
file. Double click on the External Files tab of Type 99 and select the
file it's supposed to be reading. 

I would suggest that you carefully review the example projects and
tutorials provided with TRNSYS as they can provide a lot of good
examples to help you through these basic problems. 

Jeff 

---
Jeff Thornton
President - TESS LLC
3 N. Pinckney Street, Suite 202, Madison WI USA 53703
Office: (608) 274-2577 Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton at tess-inc.com

On 08/20/2019 10:33 am, Yeyson Meza via TRNSYS-users wrote: 

> Hello Mr. Jeff Thornton, firstly I revise your comment about type 997, This type model allows the user to specify groundwater flows through a horizontal layer of soil, I try to fix this error. On the other hand, I copied the type and pegged in another project (Fig 1), but I have this problem when running the project the outlet temperature is very different from the original (Fig 2 and 3), the performance is totally different. As another option, I copied the whole project, all Type, and pegged this information in the window for the second project, but I have this problem and I don´t understand (Fig 3), why is this happening? 
> 
> Figure 1. Copy and page only the type and connect to the input building. 
> 
> Figure 2. The outlet temperature of EAHE in the project of figure 1. 
> 
> Figure 3. The outlet temperature of EAHE in the original project. 
> 
> Figure 4. Another option to copy and page and this error. 
> 
> El mar., 20 de ago. de 2019 a la(s) 09:57, Yeyson Meza (yeyson.meza90 at gmail.com) escribió: 
> 
> Hello Mr. Jeff Thornton, firstly I revise your comment about type 997, This type model allows the user to specify groundwater flows through a horizontal layer of soil, I try to fix this error. On the other hand, I copied the type and pegged in another project but I have this problem (Fig 1), the outlet temperature 
> 
> El lun., 19 de ago. de 2019 a la(s) 20:33, <trnsys-users-request at lists.onebuilding.org> escribió: Send TRNSYS-users mailing list submissions to
> trnsys-users at lists.onebuilding.org
> 
> To subscribe or unsubscribe via the World Wide Web, visit
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org [2]
> 
> or, via email, send a message with subject or body 'help' to
> trnsys-users-request at lists.onebuilding.org
> 
> You can reach the person managing the list at
> trnsys-users-owner at lists.onebuilding.org
> 
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
> Today's Topics:
> 
> 1. Re: How can I take datas the one widows TRNSYS to another?
> (Jeff Thornton)
> 
> ---------- Forwarded message ----------
> From: Jeff Thornton <thornton at tess-inc.com>
> To: "TRNSYS users mailing list at OneBuilding.org" <trnsys-users at lists.onebuilding.org>
> Cc: 
> Bcc: 
> Date: Mon, 19 Aug 2019 19:55:40 -0500
> Subject: Re: [TRNSYS-users] How can I take datas the one widows TRNSYS to another?
> 
> Dear Yeson Meza, 
> 
> If I understand your question, you can simply click on the proforma of the Type 997 model in your project and then select copy. Then activate the window for the second project and select paste. But I do have to point out that Type 997 is NOT intended to be an earth-to-air heat exchanger. Type 997 assumes a liquid inside of the pipes and not air! There are earth-to-air heat exchangers available from 3rd party vendors. 
> 
> Jeff 
> 
> ---
> Jeff Thornton
> President - TESS LLC
> 3 N. Pinckney Street, Suite 202, Madison WI USA 53703
> Office: (608) 274-2577 Fax: (608) 278-1475
> www.tess-inc.com [1]
> E-Mail: thornton at tess-inc.com
> 
> On 08/19/2019 9:13 am, Yeyson Meza via TRNSYS-users wrote: 
> Hello Master, Please I need to help me. I am simulating an Earth to Air Heat Exchanger with specific features, I finished it and I obtained the results, but in the other project, I simulated an office building. I want to know how to take the EAHE results and to apply in the building if this is in other windows. Is there a type that imported the information? or It's possible to copy the 997 EAHE type in the other project and TRNSYS recognizes the same characteristics. For more information, I attach the figures. Thanks. 
> 
> -- 
> 
> ING. YEYSON MEZA MORENO 
> Universidad Industrial de Santander
> 
> CEL: 3013672740 
> 
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org [2]
> 
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org [2]

 -- 

ING. YEYSON MEZA MORENO 
Universidad Industrial de Santander

CEL: 3013672740 

 -- 

ING. YEYSON MEZA MORENO 
Universidad Industrial de Santander

CEL: 3013672740 

_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
[2]

 

Links:
------
[1] http://www.tess-inc.com
[2]
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190820/34d29e1e/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 98765 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190820/34d29e1e/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 189813 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190820/34d29e1e/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 94141 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190820/34d29e1e/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 85440 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190820/34d29e1e/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 86744 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190820/34d29e1e/attachment-0009.png>


More information about the TRNSYS-users mailing list