[TRNSYS-users] COP curve inconsistency WW-HP
David BRADLEY
d.bradley at tess-inc.com
Tue Aug 20 07:01:57 PDT 2019
Vitor,
Check to make sure that the values you have specified as parameters
for things like the number of source temperatures - cooling match the
number of values that are actually in the data file. I have seen this
happen when I had specified (for example) that there were 10 source
temperatures in the data file when in fact there were only eight.
kind regards,
David
On 08/18/2019 14:26, Vitor Leite via TRNSYS-users wrote:
> Sorry all for the spam, but forgot to add attach the files
> ------------------------------------------------------------------------
> *From:* Vitor Leite <vitorleite95 at hotmail.com>
> *Sent:* Sunday, August 18, 2019 4:23 PM
> *To:* TRNSYS users mailing list at OneBuilding.org
> <trnsys-users at lists.onebuilding.org>
> *Subject:* Re: [TRNSYS-users] COP curve inconsistency WW-HP
> Hello Jeff,
>
> First,thanks for the answer.
>
> I isolated the heat pump into a new project, created 2 equation
> components representing source and load side flow and inlet
> temperatures but the heat pump is still having quite strange COP
> results, and I have no idea why.
>
> Here is basically what I did:
>
> Timestep: 0.1h
>
> Type 927 (parameters 15 to 18):
> rated heating capacity 177kW
> rated power: 46kW
> rated load/souce flowrate: 9.5 l/s
>
> I attached my expected performance curve according to the performance
> data from TESS library for type 927, and the results from some of the
> tests I performed.
>
> The main thing that I don't understand is why, even on the test
> project, there are so many scenarios that is in direct conflict with
> the performance data sheet.
>
> By reducing the load-side flowrate and increasing the EWT for the
> load-side, the heating COP went to above 5, when according to the
> performance curve, both scenarios should decrease COP.
> By having load-side EWT of 20 degrees C and flowrate equal to the
> rated value (9.5 l/s), the COP was near 3. By decreasing only the
> flowrate, COP increased to almost 4 (again, against performance curve).
> And last, by decreasing source-side EWT, COP increased as well, when
> it should decrease.
>
> Am I misunderstanding the system? Or I made a mistake even on the test
> project, as well?
>
> On my main project I have a storage tank added and there are no errors
> during the simulation. I think my only problem is understanding this
> COP curve.
>
> Thank you again,
>
> Vitor L.
>
> ------------------------------------------------------------------------
> *From:* Jeff Thornton <thornton at tess-inc.com>
> *Sent:* Monday, August 5, 2019 11:20 AM
> *To:* TRNSYS users mailing list at OneBuilding.org
> <trnsys-users at lists.onebuilding.org>
> *Cc:* Vitor Leite <vitorleite95 at hotmail.com>
> *Subject:* Re: [TRNSYS-users] COP curve inconsistency WW-HP
> Victor,
>
> The best thing you can do to start is to isolate the heat pump in a
> separate project and drive it with various inlet temperature and flow
> rates to make sure the performance of the machine matches the map.
> When you’re sure it’s working correctly that’ll help you track down
> what’s happening with the rest of your project.
>
> Jeff
>
> Sent from my iPhone
>
> On Aug 1, 2019, at 10:24 AM, Vitor Leite via TRNSYS-users
> <trnsys-users at lists.onebuilding.org
> <mailto:trnsys-users at lists.onebuilding.org>> wrote:
>
>> Hello everyone,
>>
>> I got the results from a simulation and I think I am getting
>> inconsistent results when comparing the heat pump COP and comparing
>> it normalized performance data sample included with the component,
>> which is the one I am currently using (type 927).
>>
>> The system is basically two identical heat pumps (50RT) being
>> controlled by a multi-stage differential controller. (which is also
>> controlling the flow rate for both source side and load side pumps).
>> So for the load side (connected to a vertical heat exchanger) there
>> is only really small changes in temperature and the flow-rate goes
>> from 0 to 0.5 to 1 following the number of H.Ps on.
>> Load side flow-rate also goes from 0 to 0.5 to 1 but there are bigger
>> temperature changes according to the demand.
>>
>> But, according to the performance data, during heating mode, the load
>> side flow-rate should no change normalized capacity and if the load
>> side temperature increases, normalized capacity should decrease.
>> Which was not what happened with my results.
>>
>> Can someone with a better understanding about H.Ps take a quick look
>> and see if this graph is reasonable compared to the performance curve?
>>
>> Thanks in advance
>>
>> <COP.jpg>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org
>> <mailto:TRNSYS-users at lists.onebuilding.org>
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190820/5aa6e329/attachment.html>
More information about the TRNSYS-users
mailing list