Marion, thanks for answering that! interesting question and not
something I had ever considered!
David
On 05/18/2018 04:44, Marion Hiller via TRNSYS-users wrote:
>
> Dear Karol,
>
> have set temperature to 20 and humidity to “relative humidity” and
> “outside”. What will be value of ventilation air humidity?
>
> * Type 56 does the following:
> Example 1:
> ambient air conditions: Tamb = 8 °C and RHamb = 80 %;
> ventilation: Tvent = 20 °C and RHvent = outside
>
> Result: Type 56 calculates the resulting absolute humidity gain by
> calling psychometrics kernel routine with that Tvent = 20 °C with
> RHvent = 80 %
>
> Example 2:
>
> ambient air conditions: Tamb = 8 °C and wamb = 0.003 kg/kg
> ventilation: Tvent = 20 °C and wvent = outside
>
> Result: Type 56 uses wvent = wamb = 0.003 kg/kg as the resulting
> absolute humidity gain
>
> * Thus, if you want to take into account the condition process
> which changes the relative humidity you have to
>
> * calculate the changed rel. humidity acc. to temperature change by
> an another component (AHU, Psychometrics) and
> * give the changed rel. humidity as an input in the ventilation type.
>
> Kind regards,
>
> Marion
>
> *-----------------------------------------------------------------------------------------------------------------------------------------------------------*
>
> *Dipl.-Ing. Marion Hiller **
> **TRANSSOLAR Energietechnik GmbH *
> *Stuttgart - Munich - New York - Paris ***
>
> *t: +49.711.67976.0 <tel:%2B49.711.67976.27> f: +49.711.67976.11
> <tel:%2B49.711.67976.11>*
>
> *www.transsolar.com/ <http://www.transsolar.com/>**
>
> **KlimaEngineering - Technologien für energieeffizientes Bauen und
> Nutzerkomfort in Gebäuden
> Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart *
>
> *Amtsgericht Stuttgart - HRB 23347**/ Steuernummer: 99073/00911 /
> USt-IdNr.: DE 152272639**
> Geschäftsführer: Matthias Schuler, Thomas Auer, Stefan Holst, Dieter
> Schnelle *
>
> *Von:*TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org]
> *Im Auftrag von *Karol Bandurski via TRNSYS-users
> *Gesendet:* Freitag, 18. Mai 2018 08:55
> *An:* trnsys-users at cae.wisc.edu
> *Cc:* Karol Bandurski <karol.bandurski at put.poznan.pl>;
> TechSupport at tess-inc.com; hotline <hotline at Transsolar.com>
> *Betreff:* [TRNSYS-users] humidity of vetilation air
>
> Dear Experts,
>
> In Ventilation Type Manager in TRNBuild there is possibility to set
> temperature of ventilation air to outside and also humidity to outside.
>
> I have set temperature to 20 and humidity to “relative humidity” and
> “outside”. What will be value of ventilation air humidity?
>
> 1)Does TRNBuild calculate that by heating up or cooling down outside
> air, to setting (20), the relative humidity also change?
>
> 2)If yes: Does TRNBuild take in to account that part of water will
> condensate if outside relative humidity is high and set ventilation
> temperature is much lower?
>
> Your respond will be helpful because it is not possible to direct
> check it by simulation.
>
> Kind regards,
> Karol
>
> --------------------------------------------------------------------
>
> Karol BANDURSKI M. Sc.
>
> Faculty of Civil and Environemntal Engeneering
>
> Division of Heating, Air Conditioning and Air Protection
>
> Poznan University of Technology
>
> www.put.poznan.pl/~karol. bandurski
> <http://www.put.poznan.pl/%7Ekarol.bandurski>
>
> https://www.researchgate.net/profile/Karol_Bandurski
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180518/e8c33df6/attachment-0001.html>
More information about the TRNSYS-users
mailing list