[TRNSYS-users] Internal gains in relation to the living area (w/ m2)
David BRADLEY
d.bradley at tess-inc.com
Tue Jun 19 09:11:15 PDT 2018
Ilyas,
Standards vary widely from country to country (and even
state/province to state/province) depending on the extent (or existence)
of energy codes. In the US ASHRAE standard 90.1 gives recommended limits
for lighting wattage in /commercial /buildings. Some areas adopt this
standard as an energy code and those limits become required limits.
Corridors are recommended to be lit with no more than 5.4 W/m2. Offices
are recommended to be lit no more than 11.8 W/m2. No recommendation is
given for a limit to equipment gains or occupancy gains because these
are too dependent on the use of the room. Typically, though, it is safe
to assume 16.1 to 21.5 W/m2 for plug load gains. ASHRAE publishes gains
from occupants performing various tasks. TRNBuild shows some of these
values in the occupancy gains screen if you click to view the tables.
Residential numbers are more difficult to track down. A program in
the US called Building America has some useful data. I do not know what
resources are available for the European context although I would be
quite surprised if they were not more extensive than what is available
in the US.
kind regards,
David
On 06/18/2018 08:29, Ilyas KHELIFA KERFAH via TRNSYS-users wrote:
> Hello;
> I am looking for standard values if it is possible for internal gains
> in relation to the livingarea (w/ m^2 ) which takes into account
> people, equipment and lightings. with the reference please.
> For the rooms:..............(w/ m^2 )
> for the corridor:............(w/ m^2 )
>
> Thank you.
>
> Respectfully.
>
> Ilyas.
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180619/96b63221/attachment.html>
More information about the TRNSYS-users
mailing list